WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT?
1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE.
2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100%
OUTPUT.
3)LINEARITY PRBS.
4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
Answer / carl_ellis
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT?
1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE.
2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100%
OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO
POINT IS WRONG.
The correct answer is 2, but number 4 also requires a span
correction.
1) The "Zero-point and 100% are correct, but not a
mid-range value" problem is a linearity problem.
2) The "Zero-point is correct, but 100% input is not giving
100% output" is a span problem.
4) The "100% output is correct but zero point is wrong" is
a zero offset AND a span problem because when the zero point
is corrected with the addition of a bias/offset, the 100%
point will shift up or down the same amount as the zero
shifted with the bias/offset correction. So the 100% point
will no longer be correct once the zero is corrected.
Hence, the zero AND the span will need to be corrected.
Carl Ellis
Measure First
Is This Answer Correct ? | 8 Yes | 2 No |
What are the charecterstics of control valve.
how many parts of valve positioner?
Someone Please tell me what are the Pre-Commissioning activities in a Thermal Power Plant for an instrumentaion Engg.
what is the formula for calculating milliampere at different pressure points for eg 4-20 ma = 3-15 psi but if i have to check the ma at 4.6 ma?
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
flow transmeter accuracy 0.075% of full scale & find ucertainty is 0.025 % so what is maximum limit band of uncertainty
Can i convert 230v ac to 24v dc by using a relay?Instead of Smps is it possible? What is relay logic in plc ?? How it works?
Why 4mA-20mA current loop selected as standard ???
Explain about P&ID diagram?
3 Answers Technip, Toyo Denki,
How we calculate orifice plat size???
I want to measure flow by using DP Tx and range is 0 to 1200 Kg/cm2 ?
what is the Instrumentation?