what should be distance between two electrical earthing pit
as per i.e.e
Answers were Sorted based on User's Feedback
Answer / vishwas bhat
the minimum distance two earthpits should be twice the
length of the earth electrode used i.e. for example
distance between 2 3meters pit will be 6mts.
Is This Answer Correct ? | 130 Yes | 17 No |
Answer / vishwas bhat
distance between two pits should not 3m bcoz there is a
tecnical reason behind it, and the reason is that when
there is some heavy earth fault and if one of the pits is
acting as a returning path for earth fault current then it
might go dry due to heat dissipation by the passing
current, and simultaneously one more heavy fault happens
then these pits will offer high resistance because they
have lost moisture and which is not desirable, hence the
distance between two 3m pits should be minimum 6mts.
Is This Answer Correct ? | 67 Yes | 12 No |
Answer / devesh mishra
The distance b/w the pits depends on,
a)Type of earthing
b)Type of Soil
In normal practise ,for solid earthing,the distance b/w the pits should be 3 mts.
Is This Answer Correct ? | 60 Yes | 19 No |
Answer / s .mariappan psr
The minimum distance of two earth Pit is two pit no of Earth electrode(Rod , Pipe , Plate).For example
1st earth Pit electrode - 3m
2nd earth Pit electrode - 3m
our two earth pit distance- 3+3=6m
According to your electrodes and requirements
Is This Answer Correct ? | 19 Yes | 6 No |
Answer / mahesh
WHAT IS THE DISTANCE BETWEEN BODY EARTH PIT AND NEUTRAL EARTH PIT?
Is This Answer Correct ? | 16 Yes | 9 No |
Answer / pramod sharma
according to bis 3043 1987 one earthing to another distance minimum 3 mtr techinacl reason is if earthing distance lass than 3 mtr than surface area is overlaping and fault curreent desipate to earth. also depend soil restivity and appplication load
Is This Answer Correct ? | 10 Yes | 4 No |
Answer / harkamal singh
1)Distance between two earthing pit depending upon soil resistance.
2)Type of earthing
3)earth fault calculating.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / vel
As per IS3043:
Distance between plate earth electrodes shall be 8 m minimum.
Distance between pipe earth electrodes shall be 5 m minimum.
Is This Answer Correct ? | 14 Yes | 19 No |
what is Use of Stones/Gravel in electrical Switch Yard??
how do you find making current and breaking current of the circuit breaker
what is back emf?
How is operate breaker failure scheme in substation
The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current
can we use IGBT as a AC-DC converting device in the applications?
why we use MV panels??? what's r all the needs
what is mean by D.O. in distribution line poles?
what type of motor are there in megger how they work.
Apparent power is expressed as V * I(Conjugate). Why not in V * I ?
what are the different pre- commissioning tests performed on distribution transformer, power cable and switchgear?????
How phase to phase voltage comes 440V.