Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what should be distance between two electrical earthing pit
as per i.e.e

Answers were Sorted based on User's Feedback



what should be distance between two electrical earthing pit as per i.e.e..

Answer / vishwas bhat

the minimum distance two earthpits should be twice the
length of the earth electrode used i.e. for example
distance between 2 3meters pit will be 6mts.

Is This Answer Correct ?    130 Yes 17 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / vishwas bhat

distance between two pits should not 3m bcoz there is a
tecnical reason behind it, and the reason is that when
there is some heavy earth fault and if one of the pits is
acting as a returning path for earth fault current then it
might go dry due to heat dissipation by the passing
current, and simultaneously one more heavy fault happens
then these pits will offer high resistance because they
have lost moisture and which is not desirable, hence the
distance between two 3m pits should be minimum 6mts.

Is This Answer Correct ?    67 Yes 12 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / devesh mishra

The distance b/w the pits depends on,
a)Type of earthing
b)Type of Soil
In normal practise ,for solid earthing,the distance b/w the pits should be 3 mts.

Is This Answer Correct ?    60 Yes 19 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / romil

It can be kept as far away from each other as possible but minimum distance may vary depending upon the length of the earth electrode used. Usually it must be at least the double of the earth electrode's length.

Is This Answer Correct ?    29 Yes 6 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / s .mariappan psr

The minimum distance of two earth Pit is two pit no of Earth electrode(Rod , Pipe , Plate).For example
1st earth Pit electrode - 3m
2nd earth Pit electrode - 3m
our two earth pit distance- 3+3=6m
According to your electrodes and requirements

Is This Answer Correct ?    19 Yes 6 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / mahesh

WHAT IS THE DISTANCE BETWEEN BODY EARTH PIT AND NEUTRAL EARTH PIT?

Is This Answer Correct ?    16 Yes 9 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / pramod sharma

according to bis 3043 1987 one earthing to another distance minimum 3 mtr techinacl reason is if earthing distance lass than 3 mtr than surface area is overlaping and fault curreent desipate to earth. also depend soil restivity and appplication load

Is This Answer Correct ?    10 Yes 4 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / harkamal singh

1)Distance between two earthing pit depending upon soil resistance.
2)Type of earthing
3)earth fault calculating.

Is This Answer Correct ?    4 Yes 2 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / vel

As per IS3043:
Distance between plate earth electrodes shall be 8 m minimum.
Distance between pipe earth electrodes shall be 5 m minimum.

Is This Answer Correct ?    14 Yes 19 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / thowsif

As per IEE Rule it should be minimum 5 Meters...

Is This Answer Correct ?    13 Yes 20 No

Post New Answer

More Electrical Engineering Interview Questions

how many earthings will be required for 1 isolator & 2 VCB, which are connected to a 1600 KVA Distribution TRansformer?

2 Answers  


The gauge indicates the number of amps, but what about voltage? How voltage rating (for wire or fuse) determined?

0 Answers  


I have 4 DG set with 1500KVA rating. system breakers are 11KV & alternator are 415 Volts. i want to Know what is max. resistance for body earthing & 415 & 11KV V Neuteal earthing. my fault current is 14 times for 2 sec.

2 Answers  


How we can measure the thickness of bus bar for a given load ? any farmula Plz elaborate clearly.

2 Answers   ITC Infotech, TCS,


What are the layers of protection over armoured cables?

3 Answers   Accenture, IOCL,


Hi, My question is our total motor load is 55 kw.so what cable size required for main supply. Please reply

1 Answers   Maryam Enterprises,


ward lconard control

5 Answers   Bhel,


what is principle operation of transformer?

9 Answers  


why voltage swells and dips in transmission line?

2 Answers  


WHAT HAPPENING TO TRANSFORMER???? i have the step down transformer rating 230/12v, power rating something.,,, ok. suppose iam giving 12v to secondary side,what will happen on primary side.,,,

6 Answers   Coastal Energen,


what's the difference between abs/inc encoders. apart from the position remembrance what are all the other differences. and what's mean by grey code.

0 Answers  


what is mean by potential and potential free contacts

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)