what should be distance between two electrical earthing pit
as per i.e.e

Answers were Sorted based on User's Feedback



what should be distance between two electrical earthing pit as per i.e.e..

Answer / vishwas bhat

the minimum distance two earthpits should be twice the
length of the earth electrode used i.e. for example
distance between 2 3meters pit will be 6mts.

Is This Answer Correct ?    130 Yes 17 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / vishwas bhat

distance between two pits should not 3m bcoz there is a
tecnical reason behind it, and the reason is that when
there is some heavy earth fault and if one of the pits is
acting as a returning path for earth fault current then it
might go dry due to heat dissipation by the passing
current, and simultaneously one more heavy fault happens
then these pits will offer high resistance because they
have lost moisture and which is not desirable, hence the
distance between two 3m pits should be minimum 6mts.

Is This Answer Correct ?    67 Yes 12 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / devesh mishra

The distance b/w the pits depends on,
a)Type of earthing
b)Type of Soil
In normal practise ,for solid earthing,the distance b/w the pits should be 3 mts.

Is This Answer Correct ?    60 Yes 19 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / romil

It can be kept as far away from each other as possible but minimum distance may vary depending upon the length of the earth electrode used. Usually it must be at least the double of the earth electrode's length.

Is This Answer Correct ?    29 Yes 6 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / s .mariappan psr

The minimum distance of two earth Pit is two pit no of Earth electrode(Rod , Pipe , Plate).For example
1st earth Pit electrode - 3m
2nd earth Pit electrode - 3m
our two earth pit distance- 3+3=6m
According to your electrodes and requirements

Is This Answer Correct ?    19 Yes 6 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / mahesh

WHAT IS THE DISTANCE BETWEEN BODY EARTH PIT AND NEUTRAL EARTH PIT?

Is This Answer Correct ?    16 Yes 9 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / pramod sharma

according to bis 3043 1987 one earthing to another distance minimum 3 mtr techinacl reason is if earthing distance lass than 3 mtr than surface area is overlaping and fault curreent desipate to earth. also depend soil restivity and appplication load

Is This Answer Correct ?    10 Yes 4 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / harkamal singh

1)Distance between two earthing pit depending upon soil resistance.
2)Type of earthing
3)earth fault calculating.

Is This Answer Correct ?    4 Yes 2 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / vel

As per IS3043:
Distance between plate earth electrodes shall be 8 m minimum.
Distance between pipe earth electrodes shall be 5 m minimum.

Is This Answer Correct ?    14 Yes 19 No

what should be distance between two electrical earthing pit as per i.e.e..

Answer / thowsif

As per IEE Rule it should be minimum 5 Meters...

Is This Answer Correct ?    13 Yes 20 No

Post New Answer

More Electrical Engineering Interview Questions

what is Use of Stones/Gravel in electrical Switch Yard??

4 Answers   Sanghi,


how do you find making current and breaking current of the circuit breaker

1 Answers  


what is back emf?

4 Answers   Bhel,


How is operate breaker failure scheme in substation

0 Answers  


The Howland current source produces a A Unidirectional floating load current B Bidirectional single-ended load current C Unidirectional single-ended load current D Bidirectional floating load current

0 Answers  






can we use IGBT as a AC-DC converting device in the applications?

2 Answers  


why we use MV panels??? what's r all the needs

4 Answers  


what is mean by D.O. in distribution line poles?

0 Answers  


what type of motor are there in megger how they work.

2 Answers  


Apparent power is expressed as V * I(Conjugate). Why not in V * I ?

0 Answers  


what are the different pre- commissioning tests performed on distribution transformer, power cable and switchgear?????

1 Answers   Reliance,


How phase to phase voltage comes 440V.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)