why overload relay is not tripped at time of starting of
motor allthough staring current is too high?
Answers were Sorted based on User's Feedback
Answer / r.c.tiwari
becouse at the time of starting motor take high current
very less duration & over load relay generaly made by
bymatelic contect elements.by matelic element take a time
for heating.so over load rely not trip at the time of
starting.
Is This Answer Correct ? | 21 Yes | 2 No |
Answer / ikab
when motor starts high Inrush current flows,
Relays are made smarter/biased to sense this Inrush current
and wait to let this current vanished. Inrush current has 2nd harmonics components and this makes it easy to recognize this current from normal current.
Is This Answer Correct ? | 6 Yes | 3 No |
Answer / simon peter
Since the starting I of the motor is high but the tripping value is rated onthe basis of short or earth fault occured.....
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / shalini
In a star delta connection, OLR will be placed in the
dealta side.
Starting current would be high during the star connection &
timer will be set to switch over from star to delta.
Once the delta connection is activated, the current would
be naturally less & therby OLR doesnot trip.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / lokesh
As simple one, we are using the starters ( DOL, Star Delta)
liket that for this purpose.
So this starter will help to start the motor with reduced
starting current.
Is This Answer Correct ? | 2 Yes | 15 No |
Why are short circuit ratings always 16kA,25kA,36kA and 50kA.Who has fixed these?
earth also having a gravitational force (magnetic field of north and south)but it attracts any object compare to this theartifical magnetic cant perform same as earth why?
What is the difference between a Distribution Transformer and a Power Transformer.
how to set time from star to delta starter
if we connect a ohmmeter across shorted capacitor .what will be the reading..will it be zero or infinity
why Line voltage =1.732XPhase voltage what mean by 1.732
how to check 3phase motor winding with help of multimeter?
why is only master neutral contactor is made to switch in synchronization of dg sets
What are the advantages of individual drives?
1 Answers A1 Electricals, Suzlon,
11KV electrical line going through the forest in cloudy night ,how can we find the direction of line.
5 Answers Bhel, Cesco, HZL, Nesco,
how to meas-our losses for L.T & H.T
what is the function of turbo charger in disel generators