why overload relay is not tripped at time of starting of
motor allthough staring current is too high?
Answers were Sorted based on User's Feedback
Answer / r.c.tiwari
becouse at the time of starting motor take high current
very less duration & over load relay generaly made by
bymatelic contect elements.by matelic element take a time
for heating.so over load rely not trip at the time of
starting.
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / ikab
when motor starts high Inrush current flows,
Relays are made smarter/biased to sense this Inrush current
and wait to let this current vanished. Inrush current has 2nd harmonics components and this makes it easy to recognize this current from normal current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / simon peter
Since the starting I of the motor is high but the tripping value is rated onthe basis of short or earth fault occured.....
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / shalini
In a star delta connection, OLR will be placed in the
dealta side.
Starting current would be high during the star connection &
timer will be set to switch over from star to delta.
Once the delta connection is activated, the current would
be naturally less & therby OLR doesnot trip.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / lokesh
As simple one, we are using the starters ( DOL, Star Delta)
liket that for this purpose.
So this starter will help to start the motor with reduced
starting current.
| Is This Answer Correct ? | 2 Yes | 15 No |
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
What is essential to prove safe isolation of electrical circuit?
What is reason of rating of transmission line multi pal of 11 like as 11/33/66/220 ? Why not use 75 kv 23 kv line in power system ?
1 Answers Apollo, Balco, Bhel, Vardhman,
In what voltage EHT works(133/132/33/66kv?
When calculation of fault current and fault Kva is to be done,why always we use per unit value and why we consider the base kva?
Why are iron cores in transformers made laminated?
I have 12MW gas engine based power plant its running parallel with grid. my problem is When cpp run in island mode(without geb) that time geb transformer power factor is 0.2 lagging. When cpp run with parallel that time power factor is 0.94 lagging So how can i maintain power factor ofgeb transformer in island mode 0.9 lagging?
how to calculate mf when meter and cTPT detail are given
How we calculat the NGR of 3phase Generator, Our generation voltage 11KV
how the testing of protection CT Testing done through Primary injection kit please describe in detail procedure...
What is excitation in case of dc motor?
Why the capcitor to be discharged after put in to operation & why not inductor though the both elements stores energy?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)