why overload relay is not tripped at time of starting of
motor allthough staring current is too high?
Answers were Sorted based on User's Feedback
Answer / r.c.tiwari
becouse at the time of starting motor take high current
very less duration & over load relay generaly made by
bymatelic contect elements.by matelic element take a time
for heating.so over load rely not trip at the time of
starting.
| Is This Answer Correct ? | 21 Yes | 2 No |
Answer / ikab
when motor starts high Inrush current flows,
Relays are made smarter/biased to sense this Inrush current
and wait to let this current vanished. Inrush current has 2nd harmonics components and this makes it easy to recognize this current from normal current.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / simon peter
Since the starting I of the motor is high but the tripping value is rated onthe basis of short or earth fault occured.....
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / shalini
In a star delta connection, OLR will be placed in the
dealta side.
Starting current would be high during the star connection &
timer will be set to switch over from star to delta.
Once the delta connection is activated, the current would
be naturally less & therby OLR doesnot trip.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / lokesh
As simple one, we are using the starters ( DOL, Star Delta)
liket that for this purpose.
So this starter will help to start the motor with reduced
starting current.
| Is This Answer Correct ? | 2 Yes | 15 No |
Can i connect all earth pits in ring system..., And wat IS 3043 says...please help me
Does the total power means fundamental plus Harmonics?
can any one suggest websites having study maetrials for the electrical students?
how to calculate H.P of a moter from speed of a moter?
How to work E.L.C.B and how to connect in circuit.
one conductor length is L.and i am strech uniformly this conductor and made length is 2L.so resistance of this strech conductor is R=4R..but i want to know about area of stech conductor hows it become a/2..
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
Can we connect two CT'S to one energymeter?
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
If Ac supply is given to the DC motor then what will happen? clear explanation
What is the difference between body earthing and neutral earthing?
Can 60 Hz transformer be used inplace of 50 hz transfromer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)