what should be distance between two electrical earthing pit
as per i.e.e
Answer Posted / s .mariappan psr
The minimum distance of two earth Pit is two pit no of Earth electrode(Rod , Pipe , Plate).For example
1st earth Pit electrode - 3m
2nd earth Pit electrode - 3m
our two earth pit distance- 3+3=6m
According to your electrodes and requirements
| Is This Answer Correct ? | 19 Yes | 6 No |
Post New Answer View All Answers
what is difference between isolation and ultra isolation transformer?, what is the method of testing ?
Compare jfet’s and mosfet’s.
What is gross error?
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
What is difference between start imitation and start interlock for 3 phase motor protection ?
What are hrc fuses and where it is used?
what is the step by step formula for calculating bus bar phase and neutral size of a panel board.suppose the incomer of panel board is 100A..???step by step answer please
can we conduct the swineburne's test on a dc series motor? why?
How many types of losses occur in a transformer?
Basic motor transformer generator
How the PF control while running DG set with load
what is Anti-pumping?
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to reconfirm its base capacity.
Explain what is electric traction? Explain few advantages of electric traction system?
why the neutral line is not giving shock to us if we touch it ?