what should be distance between two electrical earthing pit
as per i.e.e
Answer Posted / vel
As per IS3043:
Distance between plate earth electrodes shall be 8 m minimum.
Distance between pipe earth electrodes shall be 5 m minimum.
| Is This Answer Correct ? | 14 Yes | 19 No |
Post New Answer View All Answers
What size cable (based on voltage drop) is required to supply a 40 A three phase boiler if the wiring system is 75V single insulated cables installed in non-metallic rigid conduit 56m from the main switchboard? Voltage drop in the consumer's mains is 8V.
What is UPS and How do you maintain the UPS Maintenance? Brief Description on UPS maintenance.
How grounding is different than earthings?
Transmission through a short line depends on
what is the stear deltaprinceple?
LET ME NOW MORE ABOUT icu and ics for circuit breaker. how we calculate the rating of circuit breaker and i c u and ics values
what is the difference b/w ATS and HTS?
How much ph is maintained of water resistance starter for slipring induction motor ?
xpression 'document.FrmQF.myemail' [
State nyquist stability criterion.
Safety of dry type transformer
how unidirectional torque is produced in DC motor?
What are the types of piano switches?
what is capacitor voltage transformer?? how it is different from potential transformer?
what will happen if synchronous machine rotor fed from single phase ac supply