11KW Delta motor is taking about 44Amps in star and goes
upto 70Amps in delta and trips OFF. The rated current is
26Amps. Application is for the blower. The motor takes ( no
load without coupling impller ) only 2.5A and 5Amps in star
& delta starter test.Need to know why its taking high
current.
Answers were Sorted based on User's Feedback
Answer / rajendran
The motor takes very less current at no load than the
normal and when it is loaded it is taking the obnormal
currents even in delta operating mode....
it seems there must be a problem in the connections or in
the supply voltage of the mains or improper impeller
arrangement causing very high load.
probably there may be a problem in the connections only...
check the connections
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / rajesh vallem
in blower applications before starting the motor damper
should be in close position.motor concerned it is ok
because no load current of the motor is ok.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / gunasekaran
u r not explain proberly it is due to inrust current for
star phase voltage=VL/sqrt3
for delta phase voltage=line voltage so it is taking more
current than star.normally at stating motor taking 5to 6
six times of the full load current i think nothing wrong u
can incress the relay setting and then start the motor
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / boby
I think there is something wronng with imppller coupling
it alingment could be out. Because no load current of
motor is ok . So check the coupling alignment , motor
bearing and connection of input cable at main source.
| Is This Answer Correct ? | 1 Yes | 1 No |
In Blower application, starting current will be more than
normal until it gets full speed due to dampers, hence
better idea to use OLR with starting current delay time and
running current delay time setting. so that while starting
time this OLR waits for some time delay even starting
current is more than normal and trip.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / tj
Following is the check seq. :
1 Check for correct DOR/Phase Seq, ensure termination is
correct n tight.
2 Check the relay for malfunction & its type if it is
thermal then increase setting a bit more than ratd amps &
chk, n if its micro proc based then adjust the setting
acording to motor starting curve.
3 Ensure that suction damper is at min. before starting.
4 Ensure the motor is correct according to fan torque.
5 Check for any abnormal sound or play from fan side.
6 Also check the cable, it should not be underrated, causing
higher potential drop at startup.
Hope the above helps you........
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anil bhatia
check rated current as you mentioned 26 amps
according to chart it should be 19/20 amps
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / felixraj
check the coupling alignment,blower condition(bearing)
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / suraj_ojha
I am agree with mr.rajendern there is some mistake is in
their control wiring of starter.
| Is This Answer Correct ? | 0 Yes | 5 No |
can we connect PARALLEL 2 D.G set with different rating?? How ? What is the requirement for this connections?
in communication what is the role of elelctrical engineer?
what is called star connection and delta connection also purpose of this connections?
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to reconfirm its base capacity.
If I fill the form of engineering services and I left the exam de to navoidable reasons . Will it counts my one attempt
What is the difference between rulling span and wind span of of an Over Head Transmission Line?
how we can know which is Lv side and HV side of transformer by just seeing it?
whats the advandage of PMG in alternator?
What is the basic difference between 90% stator earth fault and 100% stator earth fault, and its phenmenona?
i wanna know that star point in transformer becomes as a neutral on secondary side now tell me that how is that possible?because if joit the all three winding ends with each other it can b short circuited.dut it doesn't.WHY?pls Answer me in brief.thanks alot
what is neutral ground resistance relay? how it is helpful in protecting system?
Whar is the KvA rating of 33Kv substation & actual kv rating of power generaating station.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)