what is neutral ground resistance relay? how it is helpful
in protecting system?
Answers were Sorted based on User's Feedback
Answer / ranjan prasad
Normally NGR is being connected with the neutral of
transformers or Generators to limit the the fault current.
This NGR basically gives the out put in terms of voltage
during the fault condition (like Earth Fault). To sens the
voltage during fault condition, isolation transformer is
connected across NGR for voltage feed back. This v f/b goes
to the relay to operate in case of earth fault depending
upon the setting done at relay.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / aamod tripathi
NEUTRAL GROUND RESISTANCE RELAY IS A RELAY WHICH WILL
OPERATE UNDER AN EARTH FAULT. AND WILL GET ACTIVATED IN
CASE OF AN EARTH FAULT ONLY TO ACTIVATE THE BREAKER IN
ORDER TO TRIP THE CIRCUIT.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / biswajit sahoo
THIS IS BASICALLY REF TYPE RELAY. iT WORKS ON PRINCIPLE OF
DIFFERENCE IN NEUTRAL CURRENT IE TRANSFORMER END AND
CONSUMER FEEDER END
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / angela tong
NGR is neutral ground resistance which is inserted between
neutral and ground to operate during ground fault happens.
It could prevent generator or transformer from overvoltage
or arc flash grounding transient overvoltage and clear the
fault up.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is grounding & what is the value of groumding rod 2.5m?
what is maxemo work permit procedure
how snubber circuit works to protect switching devices?
How the soft starter control the starting current in three phase squirrel cage AC Motor?
how much percentage set in transformer diffrencial relay
What is main cause of cable's terminal point burned in Lug on high temperature although lug and cable selection is ok as per stantard and also tightness is ok as per situation. so please take in deep and tell correct answer thanku.
How you calculate the repturing capacity of a HRC fuse
What is HT? And specify the range of voltage?
Sir We have a REF relay connected to 10MVA(Y-Y) Transformer.on External earth fault REF relay trips along with earth fault relay.The REF relay has no complant as we tested relay.Why is it happening?
How to choose primany and secondary side MCB
which transmission is cheaper ac or dc?
Ferranti Effect says that voltage at the receiving end is higher than that at the sending end. How is it possible?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)