If AVR fails in DG set what will be the affect?
Answers were Sorted based on User's Feedback
Answer / sachin
Failure of AVR means failure of Excitation, hence DG will
continue running but no EMF (Voltage) will be generated.
| Is This Answer Correct ? | 71 Yes | 13 No |
Answer / rajesh patel
Failure of AVR means AVR will not deliver the excitation
voltaage to the exciter winding.Hance Excitor winding will
not be able to generate any excitor voltage.So there will
be no any field votage to rotor field winding and due to
this even if DG continious running but there will be no out
put voltage
| Is This Answer Correct ? | 35 Yes | 5 No |
Answer / dharamvir punia
If AVR fails in DG sets,it means no d.C. supply recevied
by DG sets Coils, no magnetic field made & coil does`t
excited, result no output given by sets.
| Is This Answer Correct ? | 30 Yes | 6 No |
Answer / sandeep jhajhra
IF AVR fails in dg set then the exitation voltage is zero
and we do not get any output voltage.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / sunil datta
then no emf will induce, because rotor is not energized.and
rotor will not become magnet at all.
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / trilok kumar
AVR-AUTOMATIC VOLTAGE REGULATOR. AS THE NAME IMPLIES IT IS
USED FOR THE REGULATION OF VOLTAGE & VOLTAGE BUILD UP
PURPOSES.IT CONSISTS OF (VOLTAGE SENSING UNIT,VOLTAGE BUILD
UP CKT,PULSE WIDTH MODULATION CKT,etc...,).OBVIOUSLY IF AVR
FAILS THERE WILL BE NO VOLTAGE.SO DG RUNS WITHOUT VOLTAGE
AND THERE WILL BE NO LOAD.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajay
1. If the avr is not giving any output voltage ie DC to the
excitor then no voltage build up will be there.
2. If the avr is not changing the dc voltage as per load
demand then voltage variation will be observed.Which means
the automatic rerulation function of avr wrt load is not
working.Hence avr needs replacement.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / chauhanalpesh
it depends upon which type of avr is that .. if its an
static one than it will get tripped and no dc output and dg
set will not generate any voltage. but if avr having no
interlock with excitor than if avr fails than it will only
affect the regulation of voltage as excitation voltage is
already generating and being given to alternator so output
will be there but non-regulated
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / jai prakash narain singh
if avr fails,field excitation will be zero and hence no
rated voltage,but residual voltage will be always there.
dg breaker will trip due to under voltage protection .
| Is This Answer Correct ? | 5 Yes | 3 No |
What is on line ups and off line ups?
what will happen if we give a dc supply to a transformer.?
why we are using panel space heaters in different control schemes????
Can a generator runs after getting 1st stator earth fault.
what is laser diodes?
why we use primary delta connectin in hight voltage transformer
If a ACB breaker is tripping and closing problem, then what will we check internal..?
cany anyone suggest electrical wesites for providing study materials?
1.what is difference between line,neutral and earth 2.IF single phase voltage is 230v ac and what should be the voltage between line to neutral,neutral to earth and earth to line
what is the maximum load on for 10 kva & 25 kva transformer
how was the induction stove working?
which type of capacitor store high amount of energy for long time ? ( polarized or unpolarized )
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)