If AVR fails in DG set what will be the affect?
Answers were Sorted based on User's Feedback
Answer / sachin
Failure of AVR means failure of Excitation, hence DG will
continue running but no EMF (Voltage) will be generated.
| Is This Answer Correct ? | 71 Yes | 13 No |
Answer / rajesh patel
Failure of AVR means AVR will not deliver the excitation
voltaage to the exciter winding.Hance Excitor winding will
not be able to generate any excitor voltage.So there will
be no any field votage to rotor field winding and due to
this even if DG continious running but there will be no out
put voltage
| Is This Answer Correct ? | 35 Yes | 5 No |
Answer / dharamvir punia
If AVR fails in DG sets,it means no d.C. supply recevied
by DG sets Coils, no magnetic field made & coil does`t
excited, result no output given by sets.
| Is This Answer Correct ? | 30 Yes | 6 No |
Answer / sandeep jhajhra
IF AVR fails in dg set then the exitation voltage is zero
and we do not get any output voltage.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / sunil datta
then no emf will induce, because rotor is not energized.and
rotor will not become magnet at all.
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / trilok kumar
AVR-AUTOMATIC VOLTAGE REGULATOR. AS THE NAME IMPLIES IT IS
USED FOR THE REGULATION OF VOLTAGE & VOLTAGE BUILD UP
PURPOSES.IT CONSISTS OF (VOLTAGE SENSING UNIT,VOLTAGE BUILD
UP CKT,PULSE WIDTH MODULATION CKT,etc...,).OBVIOUSLY IF AVR
FAILS THERE WILL BE NO VOLTAGE.SO DG RUNS WITHOUT VOLTAGE
AND THERE WILL BE NO LOAD.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajay
1. If the avr is not giving any output voltage ie DC to the
excitor then no voltage build up will be there.
2. If the avr is not changing the dc voltage as per load
demand then voltage variation will be observed.Which means
the automatic rerulation function of avr wrt load is not
working.Hence avr needs replacement.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / chauhanalpesh
it depends upon which type of avr is that .. if its an
static one than it will get tripped and no dc output and dg
set will not generate any voltage. but if avr having no
interlock with excitor than if avr fails than it will only
affect the regulation of voltage as excitation voltage is
already generating and being given to alternator so output
will be there but non-regulated
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / jai prakash narain singh
if avr fails,field excitation will be zero and hence no
rated voltage,but residual voltage will be always there.
dg breaker will trip due to under voltage protection .
| Is This Answer Correct ? | 5 Yes | 3 No |
whats the application of voltage regulation? and whats the voltage regulation's device?
why we use to transmit the power in three phases intead of single phase ?
In Slip ring Induction Motor we use Liquid Rotor Starter for Starter Every Time Liquid Filling we need add Soda Sodium Carbonate or only Distilled water is Enough.
iii) A shunt motor runs at 70 rad/sec from a 460V supply and takes in an armature current of 100A. Resistors of 2.52 ohms and 1.64 ohms are connected in series with the armature and in parallel with the armature respectively. The field excitation remains direct from the 460V supply but the generated torque is halved. Determine the new running speed. Neglect brush voltage drop. The armature resistance is 0.4 ohms. [15]
how can we calculate ct ratings ?its any formula ?
What are the difference between normal application Transformer and Solar application Transformer?
WHAT IS DIFFERENCE BETWEEN CAPACITOR AND CAPACITANCE?
what is dc system? how getting pulse from rectifier?
A powerplant has 8 gensets operating in grid parallel mode. In one genset sometimes there is pf variation and kvar variation. The plant operates in pf mode. When this variation is observed the load is stable, voltage is also stable, freq and genset speed is also stable. How will you check the functioning of pf card. What shall be the ideal output vdc of the pfc, from there it is input to AVR?
Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?
We have three 33kv substations. All of them energised by same source.When i am checking the phase sequence between one substation to other substation (like R Phase to R Phase) by multimeter i am getting some voltage.Near to LT panels UPS panels are there. Can u explain whether any possible to happen like that. In Phase SEquencemeter is showing correctly in both substations. How is it happen. Explain me.Explain me communication signal will produce Phase difference on this case.
how to calculate slip ring induction motor stator and rotor currents??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)