If AVR fails in DG set what will be the affect?
Answers were Sorted based on User's Feedback
Answer / sachin
Failure of AVR means failure of Excitation, hence DG will
continue running but no EMF (Voltage) will be generated.
| Is This Answer Correct ? | 71 Yes | 13 No |
Answer / rajesh patel
Failure of AVR means AVR will not deliver the excitation
voltaage to the exciter winding.Hance Excitor winding will
not be able to generate any excitor voltage.So there will
be no any field votage to rotor field winding and due to
this even if DG continious running but there will be no out
put voltage
| Is This Answer Correct ? | 35 Yes | 5 No |
Answer / dharamvir punia
If AVR fails in DG sets,it means no d.C. supply recevied
by DG sets Coils, no magnetic field made & coil does`t
excited, result no output given by sets.
| Is This Answer Correct ? | 30 Yes | 6 No |
Answer / sandeep jhajhra
IF AVR fails in dg set then the exitation voltage is zero
and we do not get any output voltage.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / sunil datta
then no emf will induce, because rotor is not energized.and
rotor will not become magnet at all.
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / trilok kumar
AVR-AUTOMATIC VOLTAGE REGULATOR. AS THE NAME IMPLIES IT IS
USED FOR THE REGULATION OF VOLTAGE & VOLTAGE BUILD UP
PURPOSES.IT CONSISTS OF (VOLTAGE SENSING UNIT,VOLTAGE BUILD
UP CKT,PULSE WIDTH MODULATION CKT,etc...,).OBVIOUSLY IF AVR
FAILS THERE WILL BE NO VOLTAGE.SO DG RUNS WITHOUT VOLTAGE
AND THERE WILL BE NO LOAD.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajay
1. If the avr is not giving any output voltage ie DC to the
excitor then no voltage build up will be there.
2. If the avr is not changing the dc voltage as per load
demand then voltage variation will be observed.Which means
the automatic rerulation function of avr wrt load is not
working.Hence avr needs replacement.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / chauhanalpesh
it depends upon which type of avr is that .. if its an
static one than it will get tripped and no dc output and dg
set will not generate any voltage. but if avr having no
interlock with excitor than if avr fails than it will only
affect the regulation of voltage as excitation voltage is
already generating and being given to alternator so output
will be there but non-regulated
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / jai prakash narain singh
if avr fails,field excitation will be zero and hence no
rated voltage,but residual voltage will be always there.
dg breaker will trip due to under voltage protection .
| Is This Answer Correct ? | 5 Yes | 3 No |
What is the Diference between DYN 11 and DYN 5 .How to change the Vector group from DYN 11 to DYN 5.
What do you mean by boost voltage in case of battery charger?
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
Y phase plates are used in transmission line??? what is there need???
I want to know what is the short circuit level when 8 NOS 2000 kVA, 415v, 50hZ generator connected in paraller
Difference between SFU & FSU with advantantages & drawback?
what types battery chargers are there?wanted with details.
what will happen to the core losses if we perform the open ckt test on high voltage side of a transformer ?
difference between Ac and Dc mcb ????
what are the advantages and disadvantages of oil filled cables over XLPE cables
To measure insulation resistance of 11KV cable between core & armour, what should be the test voltage & duration?
what is the function of compressor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)