Answer / sachin
Failure of AVR means failure of Excitation, hence DG will
continue running but no EMF (Voltage) will be generated.
| Is This Answer Correct ? | 71 Yes | 13 No |
Answer / rajesh patel
Failure of AVR means AVR will not deliver the excitation
voltaage to the exciter winding.Hance Excitor winding will
not be able to generate any excitor voltage.So there will
be no any field votage to rotor field winding and due to
this even if DG continious running but there will be no out
put voltage
| Is This Answer Correct ? | 35 Yes | 5 No |
Answer / dharamvir punia
If AVR fails in DG sets,it means no d.C. supply recevied
by DG sets Coils, no magnetic field made & coil does`t
excited, result no output given by sets.
| Is This Answer Correct ? | 30 Yes | 6 No |
Answer / sandeep jhajhra
IF AVR fails in dg set then the exitation voltage is zero
and we do not get any output voltage.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / sunil datta
then no emf will induce, because rotor is not energized.and
rotor will not become magnet at all.
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / trilok kumar
AVR-AUTOMATIC VOLTAGE REGULATOR. AS THE NAME IMPLIES IT IS
USED FOR THE REGULATION OF VOLTAGE & VOLTAGE BUILD UP
PURPOSES.IT CONSISTS OF (VOLTAGE SENSING UNIT,VOLTAGE BUILD
UP CKT,PULSE WIDTH MODULATION CKT,etc...,).OBVIOUSLY IF AVR
FAILS THERE WILL BE NO VOLTAGE.SO DG RUNS WITHOUT VOLTAGE
AND THERE WILL BE NO LOAD.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / ajay
1. If the avr is not giving any output voltage ie DC to the
excitor then no voltage build up will be there.
2. If the avr is not changing the dc voltage as per load
demand then voltage variation will be observed.Which means
the automatic rerulation function of avr wrt load is not
working.Hence avr needs replacement.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / chauhanalpesh
it depends upon which type of avr is that .. if its an
static one than it will get tripped and no dc output and dg
set will not generate any voltage. but if avr having no
interlock with excitor than if avr fails than it will only
affect the regulation of voltage as excitation voltage is
already generating and being given to alternator so output
will be there but non-regulated
| Is This Answer Correct ? | 6 Yes | 4 No |
Answer / jai prakash narain singh
if avr fails,field excitation will be zero and hence no
rated voltage,but residual voltage will be always there.
dg breaker will trip due to under voltage protection .
| Is This Answer Correct ? | 5 Yes | 3 No |
Give details on how you intend to handle a challenging position you are posted to manage unexpectedly as a company staff?
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
HOW TO CALCULATE THE WIRE SIZE FOR THE GIVEN LOAD?
in 50 mw generator if field is open in full load running condition what happen and for protection which relay used?
why the genearation of electricity always in form of sine wave only ??? why not cosine wave ???
Name quantities which are not transformed in the tranformer.
how is working bearing heater?
Working of microwave oven?
why can tv operate at low voltage??
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
how to identify 3phase....r y b .A new make altnator how to identify R
how to design coil turns ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)