What is the Diference between DYN 11 and DYN 5 .How to
change the Vector group from DYN 11 to DYN 5.
Answers were Sorted based on User's Feedback
Answer / rushi n. gajjar
dyn5 test of transformer in which some condition like U,V AND W. primary and sec. side we check
1U2W=1U2V;
1W2V<1W2W
1V2V=1V2W we found all this condition in dyn5 test.
dyn11 is vector diagram of 3 phase xmer phase difference 60 degree between R ND Y same way....
| Is This Answer Correct ? | 21 Yes | 8 No |
Answer / kobena wiredu
DYn means a delta-star connected transformer in which the primary is delta connected and the secondary is star connected. The number that follows tells us the position of the Red phase of secondary relative to the primary using the clock (primary Red phase at 12oclock).So Dyn11 means secondary is on the 11 oclock line and hence leads the primary by 30deg since anticlockwise is the convention.To convert from one DYn to the other you need to change both primary and secondary connections. You do this by drawing vector diagrams. By using vector diagrams i find that converting from Dyn11 to Dyn5 means: Change ABC to ACB and change abc to cba.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / hemant dehariya
In DYN 11 & DYN 5 is DYN 11 is HV voltage is lead from LV by angle of 30 degree and in DYN 5 HV voltage leg fron LV voltage by 150 degree.we can change vector group from DYN 11 to DYN 5 by change primary winding connection of transformer.
| Is This Answer Correct ? | 21 Yes | 19 No |
Why efficiency of generator is higher than motor at a particular load?
How is operate breaker failure scheme in substation
What is the function of earthfault relay?
18 Answers MultiTech, Tech Mahindra,
What type of DC Generator is used for Arc Welding purposes?
I would like to install the largest KW alternator to a 200 amp aluminum bus box in my home. Is it possible to install a 250 KW 400v 251amp synchronous alternator to my home?
how to identify the failer of igbt
what are all the preventive maintainance carried out in DG?
What current can be carried by 25 sqmm copper cable safely?
1.What is wind span ,wight span and normal span, and what is the difference for 132kv transmission .
only some transformers and some generator requires NGR why?
Actually why the transformers are rated in KVA.?
magnetizer priciple
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)