What is the Diference between DYN 11 and DYN 5 .How to
change the Vector group from DYN 11 to DYN 5.
Answers were Sorted based on User's Feedback
Answer / rushi n. gajjar
dyn5 test of transformer in which some condition like U,V AND W. primary and sec. side we check
1U2W=1U2V;
1W2V<1W2W
1V2V=1V2W we found all this condition in dyn5 test.
dyn11 is vector diagram of 3 phase xmer phase difference 60 degree between R ND Y same way....
| Is This Answer Correct ? | 21 Yes | 8 No |
Answer / kobena wiredu
DYn means a delta-star connected transformer in which the primary is delta connected and the secondary is star connected. The number that follows tells us the position of the Red phase of secondary relative to the primary using the clock (primary Red phase at 12oclock).So Dyn11 means secondary is on the 11 oclock line and hence leads the primary by 30deg since anticlockwise is the convention.To convert from one DYn to the other you need to change both primary and secondary connections. You do this by drawing vector diagrams. By using vector diagrams i find that converting from Dyn11 to Dyn5 means: Change ABC to ACB and change abc to cba.
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / hemant dehariya
In DYN 11 & DYN 5 is DYN 11 is HV voltage is lead from LV by angle of 30 degree and in DYN 5 HV voltage leg fron LV voltage by 150 degree.we can change vector group from DYN 11 to DYN 5 by change primary winding connection of transformer.
| Is This Answer Correct ? | 21 Yes | 19 No |
in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?
any earth foult trip the relay but in welding time not trip by earth foult
0 Answers Power Grid, Siemens,
What are test values for an 63 KVA and 100 Kva Distribution Transformers for the following typical tests 1)Magnetic balance 2)Short circuit test 3)Open Circuit test 4)Vector group confirmation test .please give me the standard values for all the above tests.
What is vaccum currcuit breaker.define with cause and where be use it device?
How does CT can measure the high value DC current?
How power factor of a transformer is calculated
In dc ckt. 24v or 110v, which one is more efficient and why?
Q-1 what are the structural and operational difference between a distribution and a power transformer? Q-2 what is skew in motors? Q-3 draw equivalent circuit of transformer Q-4 explain with phasors how pf is improved with loading in induction motors Q-5 DIFFERENT METHODS OF CABLE LAYING(interviewer asked if i heard new chemical based earthing system next) Q-6 pi model of medium length trans line Q-7 v/f control?why Q-8 vacuum circuit breaker operates in?
what is leading power?
How to calculate the sag on transmission Lines.
What is an 86-P or an 86-A trip
what is the transformer turn ratio formula and give some examples?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)