Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


To measure insulation resistance of 11KV cable between core
& armour, what should be the test voltage & duration?

Answers were Sorted based on User's Feedback



To measure insulation resistance of 11KV cable between core & armour, what should be the test ..

Answer / v.senthilkumar

To measure insulation resistance of 11KV cable between core
& armour, we can use 5kv megger for 60 Sec.

Is This Answer Correct ?    22 Yes 2 No

To measure insulation resistance of 11KV cable between core & armour, what should be the test ..

Answer / thowsif_emerson_csm team

To measure insulation resistance of 11KV cable between core
& armour,

Test voltage is 28KV(RMS Value)
Duration is 300 Sec...

Is This Answer Correct ?    10 Yes 6 No

To measure insulation resistance of 11KV cable between core & armour, what should be the test ..

Answer / narendra sharma

11 kv cable resistance we can measure

Test voltage is 10 kv to 20 kv (RMS Value)
And time is depend on which voltage you are selected.
if 10 kv then time should be 120 sec..........
And resistance valu also going opposit to voltage..
if suppose volt is 10 kv then megger valu 2gomh, And if volt
20 kv and valu 1gomh then cable is ok both are same valu....

Is This Answer Correct ?    4 Yes 1 No

To measure insulation resistance of 11KV cable between core & armour, what should be the test ..

Answer / sujeet pandey

To measure the insulation resistance of 11kv cable, we need
to keep Megger test voltage at 1kv and take 2 readings; one
at a interval of 15 sec and other at an interval of 1 min.
This will give Absorption Factor which is equal to ratio of
resistance at 1 min to the resistance at 15 sec. If the A.F.
is less than 1.2(a/c to Indian Standards) then the
insulation is not good and we must take the remedy action.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

what is the effect when the shunt field winding is opened in dc shunt motor (i) at the time of starting ? (ii) in running condition ?

4 Answers  


Diagram on interconnectivity of 11kv transformer with RMU (i.e, one incoming and two outgoing or two incoming and one outgoing)

0 Answers  


What is Ton Capacity of Air Conditioner?

1 Answers   TATA,


I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?

0 Answers  


What are the section criteria for cables. Now everywhere XLPE power cable is used or PVC is also used?.

0 Answers   DAE,


How cable from Kit-Kat to main switch, from starter to motor are designed?

0 Answers  


Draw SLD feeding from the SS up to distribution board of the load, calculate cable size, breaker sizes, and meter for the following case: Ground Floor: electric room, pump room, 5 shops, each is 15 KW First Floor: 5 shops, each is 15 KW Second Floor: showroom 30 KW Service Loads: water pump 3 KW (3ph) , fire pump 3 KW (3ph), and one DB service 12 KW (3ph).

0 Answers   FEWA, HMK,


what is difference between 2wire method and 4wire method of winding resistance testing of transformer?

1 Answers  


what is harmonics?

1 Answers   powercom,


What will happen if 60 Hz rated transformer is connected to the supply of 50 Hz say 415 V (3-phase) step up to 3.3 kV...?? ?

2 Answers   Essar,


how to mention 5mw generator in kva ? gen voltage is 11kv

6 Answers  


WHAT IS DIFFERENCE BETWEEN idmt and instentanous relay? is idmt is used as back up protection or else?or when instantenous relay saturates IDMT will operate???

1 Answers   BK, REL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)