To measure insulation resistance of 11KV cable between core
& armour, what should be the test voltage & duration?
Answers were Sorted based on User's Feedback
Answer / v.senthilkumar
To measure insulation resistance of 11KV cable between core
& armour, we can use 5kv megger for 60 Sec.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / thowsif_emerson_csm team
To measure insulation resistance of 11KV cable between core
& armour,
Test voltage is 28KV(RMS Value)
Duration is 300 Sec...
| Is This Answer Correct ? | 10 Yes | 6 No |
11 kv cable resistance we can measure
Test voltage is 10 kv to 20 kv (RMS Value)
And time is depend on which voltage you are selected.
if 10 kv then time should be 120 sec..........
And resistance valu also going opposit to voltage..
if suppose volt is 10 kv then megger valu 2gomh, And if volt
20 kv and valu 1gomh then cable is ok both are same valu....
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sujeet pandey
To measure the insulation resistance of 11kv cable, we need
to keep Megger test voltage at 1kv and take 2 readings; one
at a interval of 15 sec and other at an interval of 1 min.
This will give Absorption Factor which is equal to ratio of
resistance at 1 min to the resistance at 15 sec. If the A.F.
is less than 1.2(a/c to Indian Standards) then the
insulation is not good and we must take the remedy action.
| Is This Answer Correct ? | 0 Yes | 1 No |
How much current can a 3-1/2 core 100 mm wire carry?
3 Answers Epitome, Focus, Focus Energy,
what is the different between RCCB & ELCB
how to make neutral to ground voltage less than 5v? my house is under the high voltage transmission line so,proper grounding using rod salt n coal doesnt help me..so wat i do as i cant operate my computer ..this high voltage cause great problem to the motherboard i already two times replaced it.in my house voltage is coming near to 25 v between ground and neutral.plz kindly post ur answer to my email id manish77777@gmail.com ..
In an ideal transformer no load primary current I0 A lags behind V1 by 90 degree B is in the phase with V1 C leads V1 by 90 degree D lags V1 by 45 degree
why we are calculating the capacitance between phase(conductor line)and ground in transmission line?why cant we calculate capacitance between the phase and the nuetral line?if so what is procedure.
What is the intent of short circuit studies?
5. What is PMG in Alternators?
low voltage grounding is done by?? 1)solidly gnd 2)ressistance 3)reactance
This is reqd for a 1MW Solar power plant..We have 2DC outputs from the solar panels Connected to 2INVERTOR panels.. Output from invertor is 3ph,280v,500kva,50hz.These are connected to individual ACB.This has to be stepped up to 11KV ,1250KVA SYSTEM.Now can I use (1) one more ACBTO GIVE A COMBINED OUTPUT OF 1000KVA,280V & STEP UP THE OUTPUT BY USING a single two winding 3 ph transformer 11kv/1250kva. or (2)use the two outputs and connect to one three winding transformer of above rating..Pls suggestwith details.
what happens if dc supply is given and the remedies for it.
if two bulb of 50w &30w apply in series having 230v the which bulb glow bright ,why
how to calculate transformer turn primary & secondary side 11kv to 420v
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)