To measure insulation resistance of 11KV cable between core
& armour, what should be the test voltage & duration?
Answers were Sorted based on User's Feedback
Answer / v.senthilkumar
To measure insulation resistance of 11KV cable between core
& armour, we can use 5kv megger for 60 Sec.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / thowsif_emerson_csm team
To measure insulation resistance of 11KV cable between core
& armour,
Test voltage is 28KV(RMS Value)
Duration is 300 Sec...
| Is This Answer Correct ? | 10 Yes | 6 No |
11 kv cable resistance we can measure
Test voltage is 10 kv to 20 kv (RMS Value)
And time is depend on which voltage you are selected.
if 10 kv then time should be 120 sec..........
And resistance valu also going opposit to voltage..
if suppose volt is 10 kv then megger valu 2gomh, And if volt
20 kv and valu 1gomh then cable is ok both are same valu....
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sujeet pandey
To measure the insulation resistance of 11kv cable, we need
to keep Megger test voltage at 1kv and take 2 readings; one
at a interval of 15 sec and other at an interval of 1 min.
This will give Absorption Factor which is equal to ratio of
resistance at 1 min to the resistance at 15 sec. If the A.F.
is less than 1.2(a/c to Indian Standards) then the
insulation is not good and we must take the remedy action.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the effect when the shunt field winding is opened in dc shunt motor (i) at the time of starting ? (ii) in running condition ?
Diagram on interconnectivity of 11kv transformer with RMU (i.e, one incoming and two outgoing or two incoming and one outgoing)
What is Ton Capacity of Air Conditioner?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
What are the section criteria for cables. Now everywhere XLPE power cable is used or PVC is also used?.
How cable from Kit-Kat to main switch, from starter to motor are designed?
Draw SLD feeding from the SS up to distribution board of the load, calculate cable size, breaker sizes, and meter for the following case: Ground Floor: electric room, pump room, 5 shops, each is 15 KW First Floor: 5 shops, each is 15 KW Second Floor: showroom 30 KW Service Loads: water pump 3 KW (3ph) , fire pump 3 KW (3ph), and one DB service 12 KW (3ph).
what is difference between 2wire method and 4wire method of winding resistance testing of transformer?
what is harmonics?
What will happen if 60 Hz rated transformer is connected to the supply of 50 Hz say 415 V (3-phase) step up to 3.3 kV...?? ?
how to mention 5mw generator in kva ? gen voltage is 11kv
WHAT IS DIFFERENCE BETWEEN idmt and instentanous relay? is idmt is used as back up protection or else?or when instantenous relay saturates IDMT will operate???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)