If AVR fails in DG set what will be the affect?
Answers were Sorted based on User's Feedback
Answer / magoola faruku
AVR MEANS AUTOMATIC VOLTAGE REGULATOR-BUT works hand in
hand with the thyristor bridge responsible for
transforming the ac to dc which is used in generating the
ac voltage and at the same time uses the feed back lines
from the output of main ac in line with what is set to
varify wether the ac as per set is ok or not. if not ok avr
requests the bridge to send a more dc or if less then
request to reduce on the dc and as such carrying out the
function of regulation
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vivek g. acholkar
In D.G. set Excitation field is used for generate Voltage.
AVR is used to control Excitation field.If AVR fails the
Voltage will be not generated by D.G.set,but due to residual
magnetism it will running.(If there not available any auto
system to shut down Engine.example--POWERCOM )
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sheikh
DG set AVR Failed means no excitation voltage to generator
then generator ouput e.m.f also will be 00 volts.in this
case generator should goes to shut down in safety of under
voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / malik
AVR is auto voltage regulator that simply means it regulate
the voltage.so if it fails we have to face over voltage
problem.if we want to cheack AVR is faulty or not we have
to bypass AVR by using battry.
| Is This Answer Correct ? | 0 Yes | 3 No |
Answer / big bull
It depends on whether the DG is connected to grid (infinite
bus) or stand alone. If it is stand alone, there is no
harm, there won't be any terminal voltage. But if the DG is
connected to grid then on loss of field generator draws
reactive power from grid to maintain terminal volatge. As
DG losses the field, it tends to over speed and behaves as
an induction generator.This may cause stability issues with
grid if the grid is small. also
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / rahul shukla
if AVR OF DG SET FAIL THEN EMF=0 AND DG WILL BE INDUCTIVE
LOAD IT WILL DRAW REACVE POWER FROM GRID .
| Is This Answer Correct ? | 14 Yes | 21 No |
Answer / lokesh
if AVR fails in DG sets emf production will be zero signal
will be sent to Governer engien will shut down
| Is This Answer Correct ? | 9 Yes | 25 No |
What is Exact meaning for Full load Efficiency and Maximum Efficiency of Transformer? Is there any Difference between? If yes ,please provide with formulae?
can we find the inductance of a induction motor?
what is used root two in single phase line?
what r the main parts of central chiller plant in Air conditioner ? explain the function of each?
if two transformers are parallel & both have fault short ckt. impedance of 50KA in each case will it increase or decrease show example?
I have a 600VA UPS for computer only. It holds for 20minutes only. 1. Can it be upgraded for longer period.? 2. Can it be used for one ceiling fan and a tube light? If yes, how to upgrade?
how can calculate static 3phase 4wire CT & PT operated energy meter constant when calibrating using refference meter suppose we have 11kv/110v PT and 30/5A CT, the meter constant is 160imp/kwh, where meter is showing MW energy? give me solution which constant i feed in my refference meter for calibration of energy meter?
sail kaott diploma ece ke interviw me qus.kis parkar ke aate hai aur G.S me kya puchate hai kya sameedyaan me kis parkar ke qu.puchate hai
My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I - is the value of AC fault current. t - is the operating time of disconnecting device in seconds. K – is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.
Explen all type electrical protection ? like O/C,E/F,NPS,VOLTAGE UN BLANCE,CURRENT UN BALANCE,NAGETIVE PHASE SEQ,AND ETC...............electrical Protection
why phase & neutral is use in tv? why earthing not use ?
why need of ac exietation in alternater.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)