I want to know what is the short circuit level when 8 NOS
2000 kVA, 415v, 50hZ generator connected in paraller
Answer / s c budhiraja
Taking 10% impedence of one gen.the faut level of one gen
will be 16000kva or 2.8KA at 415 Volts.the faut level for
eight generators will be 2.8x8=22.4KA
| Is This Answer Correct ? | 2 Yes | 4 No |
What is working of Trip Ckt.Supervision Relay?
toughest decision you ever had to make
why ac supply neutral should earth not in dc (-)
How to back charge the Gas turbine generator
explain transformer ct connection?
How Can I calculate for the photometrics requirements for a street lighting? Data given are: 45 units of 6 meter light pole with 150 watts metal halide lamp, 220 volts and installed in a promenade area.
What are reasond for high wattage in single phase induction motors
63MVA,220KV/6.9KV Transformer LV side neutral is connected to Earth pit through NGR. Whether this earth pit required to connect with near by below grouding earth mat or it is to be kept separate?
what is purpose of using reactor in substations
What is the rating of HT SUBSTATION and LT SUBSTATION?
what is inverter and converter
7 Answers Shrishti Power Technologies,
will a transformer work when pulsating dc id applied to its primary?? what will be the result??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)