I want to know what is the short circuit level when 8 NOS
2000 kVA, 415v, 50hZ generator connected in paraller
Answer / s c budhiraja
Taking 10% impedence of one gen.the faut level of one gen
will be 16000kva or 2.8KA at 415 Volts.the faut level for
eight generators will be 2.8x8=22.4KA
Is This Answer Correct ? | 2 Yes | 4 No |
Supose we have one 220v A.C fan.if we provide 220v D.C what will be happen?
what about GD square and its important for motor design?
primery try cell?
We have two Al.busbars each of size 125mm*10 mm connected in parallel.To increase the current rating ,can we connect third busbar of size 100mm*10mm in parallel to existing two busbars?In my opinion ,if we connect busbars of different sizes in parallel,then the busbar of lowest size will take much current.So this type of paralleling should be avoided .Am I correct?
Please explain open transition and closed transistion system in Star delta Starter?and also the state difference of both?
What does CDG,CDAG,CAG,VAJ,VAJH,VTT,VAZ,VAA etc. stands for in case of relays and can anyone answer to decode this codes C,V,D,G,A,X,TT,J,JH etc
what is the safety of voltage power transformer(2250KVA0
200-100/1-1A – Transformer Knee point voltage
I have 380.KVA Volva Penta DG set. Tell me how to calculate units from KWH reading....
Differenciate between circuit wiring and sub main wiring with illustrations
What are disadvantages of capacitor
Can we use LT(150 sq. mm) cable in place of HT (120 sq.mm.) cable.?