how can we minimize the off load losses of a distribution
transformer which is required to be energized 24x7 ??
capacity of the T/F is 1250 KVA and off load losses are
around 2.0 KW.. can we use capacitor bank at the secondary
of such a T/F to overcome off load losses? please elaborate
briefly...thanks
Answers were Sorted based on User's Feedback
Answer / ahmad yousuf
need answers from Transformer specialists..!!
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shariff
Distribution transformers are to be charged 24x7 as they
have to supply to the consumers. These transformers are
loaded in a day ( 24 hrs) with different loads, i.e more
load during peak hours and light loads during off peak
hours. Whatever the load or no load on this trf the off
load losses will be present in the trfs and cant be
avoided. The capacitors connecting sec. will not help in
any way and that will be used only for the pf improvement.
Hence this trf efficency will be calculated as ALL-DAY
EFFCICIENCY... For more the the effciency the trf should be
loaded to its rating(100%). The noload (offload) losses
cant be supressed in the transformers as this is part of
the loss occurred to magntize the core.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is two point starter?
I have a small system with two motors that are running on 380 vac, 60 hz. These motors are expensive and I usally get them from Brazil. I am adding another motor to the system, but I want to purchase a 480 vac, 60 hz motor to use. It will be on a VFD that is rated fro 380 thru 480. Is this posible and will I have to use a larger motor and derate it?
0 Answers US Electrofused Minerals,
why in motors dc extitaedtion is prefer
what are upstream faults and downstream faults in power system
generally rectifying of ac tells. ac signel appear at phase and neutral with respect to frequency by -veand +cycles. but we doesn't experience shock with neutral in house hold ac??????.
when current lags behind voltage how does it affect the circuit.In other words what is the significance of lagging current?
how to calculate the mesh earth network resistance in such substation, is there any recommended resistance values with references , thanks!
Is there any Institution (Not AMIE)for giving B-Tech/M-tech in Electrical engineering for those who r in service? Give the details please.
What are the special protection given for high capacity Motor, more then 10mw
What is the fault or needs to be done when frequency in ac drives is not changing?
Hi! iam Rajanikanth.Can u tell me FAQ's of AP TRANSCO.
How select ELCB for 32amp. socket having quantity 12Nos. We have to do this wiring in PLANT. Please Also explain the incoming cable specification.
0 Answers Gulf Industrial Services Company GISCO,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)