Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD
EVEN AFTER IT IS DE ENERGISED

Answers were Sorted based on User's Feedback



HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED..

Answer / dhandapani muthu.r, je tneb, i

Unless otherwise it is discharged and earthed it should be
treated as energised. We have to discharge and eath that
bus or cable with a set of earth rods. Then only it is
proved. We could also use a remote sensor to prove that it
is dead.

Is This Answer Correct ?    13 Yes 3 No

HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED..

Answer / rod

As we are dealing with high voltage it is critical that the
correct procedure is used. 1/ A switching sheet should be
used to ensure that both sides of the test point is
isolated locked and tagged, 2/ A Modiwak (HV sensor) should
then be tested on a known live source first then the
isolated point should be tested and the Modiwak should then
be retested on the known live source, this ensures that the
Modiwak is functional, 3/ Then dressed in the correct PPE
earths may be installed, making sure the the earths are of
a size for the fault level at that point.
All the previous answers are partly correct but to prevent
accidents it is esential that a strict procedure is used.

Is This Answer Correct ?    8 Yes 0 No

HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED..

Answer / hassan

BOTH SIDES BREAKER OPENED , DE-ENERGIZED AND EARTH APPLIED.

Is This Answer Correct ?    7 Yes 3 No

HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED..

Answer / giri

Nowadays we have got HT sensors which will give indication
when it is brought near the live bus bar.

Is This Answer Correct ?    3 Yes 0 No

HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED..

Answer / kedar

After taking all the necessary steps to discharge the bus-bars even then u r not confirmed. Then you should use a special meter which works on induction principle which senses the magnetic field of the bus bar and will tell u whether the bus is discharged or not.

Is This Answer Correct ?    0 Yes 2 No

HOW DO YOU PROVE THE HIGH VOLTAGE CABLES OR BUSBAR IS DEAD EVEN AFTER IT IS DE ENERGISED..

Answer / siddharth tayade

unless there is nothing any potential refrence to earth and
bus

Is This Answer Correct ?    0 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

why a three phase transformer cant rotate like three phase motor

7 Answers  


Why we are checking the vector group & turn ratio of Xformer while PM?

1 Answers  


What is the accepted limit to increase the choosen transformer capacity over the load and why ?

1 Answers  


can we start slipring motor on star delta like we start induction motor ? if yes where will we connect ?

0 Answers   NovaTech,


how to calculate the cable size for LT and HT power cables with detail explanation?

2 Answers   Asset Developments, Bhel,


How to distinguish between the armature wires with the field wires of a Dc motor ?

5 Answers  


why told ' x ' mer to transformer

1 Answers   Electrotherm,


We wish to test 60 Hz systems from a 50 Hz supply. To acheive frequency conversion, we use a VFD. The VFD powers 40 kVA transformer, which has motor and non-motor loads on it. Will the transformer work?

2 Answers   Suzlon,


How do we check transformer losses and what are the ways to minimise it.

5 Answers  


Power factor =1.000 at factory in supply. However, PF = 0.8 at motor end. Current = 100 Amp, Voltage = 400 V. What is the power distribution loss? Can I reduce it by adding capacitor at the load feeder?

0 Answers   Accenture,


In power generator sets, when they are coverted from 50hz to 60hz, the kva rating after conversion increases. For example, the manufacturer of a perkins 200kva @ 50Hz generator set has mentioned it to become 220kva after converstion to 60hz. What is the relation between the frequency & the KVA rating. Any formula please.

3 Answers  


what is voltage ?

7 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)