why a three phase transformer cant rotate like three phase motor
Answers were Sorted based on User's Feedback
Answer / gajanan
there are 2 reasons
1. the windings of motor are displaced in space and phase
but that of xmer are only in phase.
2. the windings of xmer are concentrically connected and in
conc conneced wind no mechanical motion is produed
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / nithi
Three phase transformer cannot rotate like 3phase motor.becoz,
1.There is no mechanical displacement of winding.so,no
rotating magnetic field.
2.There is no air-gap b/w py & sec winding.
| Is This Answer Correct ? | 9 Yes | 10 No |
Answer / jay
A current carrying conductor rotates only when it is placed in an external rotating magnetic field. Therefore there are two parts in any motor i.e. rotor and stator, one for the purpose of field and other for rotation. although there is a rotating field in a 3 ph transformer the flux and the magnetic field is the same (mutual flux). for the force there should be external magnetic field,current and conductor itself. As there is no external field all the pr and secondary winding do is to induce voltages.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / suresh
the primary and the secondary are the same frequencyin the
case of three phase transformer where as
in the same frequency the induction motor canot rotate
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / a.ashraif
Because Transformer works on the princle of mutual
induction moreover it is a static device not an rotating
device and also it is only capable of stepping up or step
down of voltage so only it cant rotae like a three phase
motor
| Is This Answer Correct ? | 12 Yes | 16 No |
Answer / shilpa
because unlike an induction motor the secondary is not
provided with a shaft and mechanical arrangements making it
able to rotate . otherwise th e induction motor also works
on the same principle and rotates.
| Is This Answer Correct ? | 3 Yes | 12 No |
Because Transformer only transfer load from higher level to
lower level in technical can say Transformer can stepup and
step down the voltage. so, this is call static device not
moving device.Configuration of transformer is Dry type Oil
type for distribution of load with diffent cooling
process . Three phase motor has rorating field through
shaft of motor.Due to this cause transformer rating always
in ative load (KVA) not in Real Load (KW).and Motor has
name with real load and HP rating.
| Is This Answer Correct ? | 3 Yes | 13 No |
if we look on phasor of the transformer vaoltage is 180 oppsite at primary and the secondary so to improve a power factor is secondary should kept negative to improve it primary side means is -.90 became +.90 at other side
why CT ratio stand for 50/5, 100/5, 25/5.
If we have to find the inductance of a dc shunt motor then by giving dc supply or ac supply and what is the reason for it. (this example is from "to determine the transfer function of a dc shunt motor ")
If the t/f capacity is 500KvA then what is Amps ratting of the main breaker.
what is the power factor of the megnetising component of transformer
What is the reason behind 11kv 33kv 132kv.....means multiple of 11?
What is proportional controller?
What are the advantages of hydropower?
WHAT MEANT BY MCC PANEL?
what is the difference between surge arrestor and surge supressor
Why do we apply both Differential and REF (HV and LV) protection schemes on YNyn configuration of a transformer?
What can be a rating of a transformer(KVA) if the load is about 1000KW?illustrate by showing formula?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)