In power generator sets, when they are coverted from 50hz
to 60hz, the kva rating after conversion increases. For
example, the manufacturer of a perkins 200kva @ 50Hz
generator set has mentioned it to become 220kva after
converstion to 60hz. What is the relation between the
frequency & the KVA rating. Any formula please.
Answers were Sorted based on User's Feedback
Answer / guest
Increased freq will increase EMF generated which in turn
will increase KVA rating.
| Is This Answer Correct ? | 4 Yes | 1 No |
If they increase frequency of the supply means perfomence
of the load will increased. number of cycles per second is
increased. that mean speed of the motor (load) is increased.
| Is This Answer Correct ? | 2 Yes | 1 No |
The main reason for the increase in the kva is that the
diesel engine produces more HP at 1800 rpm than at 1500 rpm.
This allows a higher kw output. The alternator can also
handle the higher current and therefore the kva is
increased. Note that the rated power factor stays the same.
This is because the amount of cooling air is increased at
the higher speed.
The increase in the EMF per turn allows a higher voltage to
be generated but this is reduced by the AVR reducing the
excitation. This has no effect on the kva capacity of the
generator set.
| Is This Answer Correct ? | 0 Yes | 0 No |
There are a Transformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
When calculation of fault current and fault Kva is to be done,why always we use per unit value and why we consider the base kva?
How are calculated the aluminium busbar cross section area?
what is mutual induction principle?
In our factory so many iron pillors are exists for supporting the shed/Hangar. If do more no of earthings at one piller instead of doing more earth pits in many locations and running earth strip around the hanger, I can save the money. Please suggest this method is acceptable as per Is specifications though the Earth resitance of the farthest piller is with in the limits as per IS specifications.
what material is the electrical housing wire made of? is there any difference for the telephone lines?
what is excitor response of an excitor?
Dir sir we have 750 kva Caterpillar dg set we are fas on different problem we start dg set ofter 1 mint apply load around 500a dg was run one or 3 mint after 3 mints dg was shutdown automatic how to face tis problem
what is the function of statics switch in ups and tell me parts
I have 725KVA DG set how to Calculate the Ratio of KWH? Whatb is the Formila
what is dc voltage?
Why 11KV/440V distribution supply use for Domestic use?
3 Answers Essar, Getco, Nissan,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)