In power generator sets, when they are coverted from 50hz
to 60hz, the kva rating after conversion increases. For
example, the manufacturer of a perkins 200kva @ 50Hz
generator set has mentioned it to become 220kva after
converstion to 60hz. What is the relation between the
frequency & the KVA rating. Any formula please.
Answers were Sorted based on User's Feedback
Answer / guest
Increased freq will increase EMF generated which in turn
will increase KVA rating.
| Is This Answer Correct ? | 4 Yes | 1 No |
If they increase frequency of the supply means perfomence
of the load will increased. number of cycles per second is
increased. that mean speed of the motor (load) is increased.
| Is This Answer Correct ? | 2 Yes | 1 No |
The main reason for the increase in the kva is that the
diesel engine produces more HP at 1800 rpm than at 1500 rpm.
This allows a higher kw output. The alternator can also
handle the higher current and therefore the kva is
increased. Note that the rated power factor stays the same.
This is because the amount of cooling air is increased at
the higher speed.
The increase in the EMF per turn allows a higher voltage to
be generated but this is reduced by the AVR reducing the
excitation. This has no effect on the kva capacity of the
generator set.
| Is This Answer Correct ? | 0 Yes | 0 No |
If one d.g. is unable to take full load of system, then second d.g. will take care of partly Load.for this condition RPM of both DG set should be equal.By using Synchronization panel RPM of dg sets are match, is it true?
can we run three phase motor by single phase? and what happens if we do this
What is the unit of charge and current?
How can calculate ups battery back up time?
25 Answers Cisco, Cooper, Pronet, Wipro,
what is "pu" in electrical engg.
What is resistance reading of earth copper rod with grid and without grid?
what is relation between HP & BHP
Whay you want to change your job.
i m in need of current rating chart of heavy duty pvc/xlpe, cu/al cables. can somebody provide me? if yes, plz send me at ashish_patel111@yahoo.com
Why induction motor can not be operated at synchronous speed?? what would happen if it is operated at synchronous speed??
what is tha between elcb & rccb?
We are using 3core 11KV HT cable for same phase for generator outgoing, the cable leakage current is high and cable heated overly what is the remidy, if we use the 3core cable for 3phases the problem is solved are not?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)