How do we check transformer losses and what are the ways to
minimise it.
Answers were Sorted based on User's Feedback
Answer / guest
transformer losses can be found by doing open circuit test
and short circuit test
open circuit test gives the core losses
short circuit test gives the copper losses
note in open circuit test the lv side is given supply and
in short circuit test the hv side is given supply
the iron losses can be reduced by providing laminations of
thinner dimension and using c.r.g.o sheet for laminations
the copper losses depend on the winding resistance which
increases due to heat can be reduced by providing
sufficient cooling to the winding.
| Is This Answer Correct ? | 36 Yes | 2 No |
Answer / manthesh.patil
we can check transformer losses by short ckt and open ckt test
,for checking cu loss we use short ckt test and for iron
loss we use open ckt test..to reduce copper loss we should
go for good cooling and for iron loss the core should be
perfectly laminated
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / sumitgarg
we can check a trans losses by open circuit and short
sircuit test.
to minimise these losses we shuold have a good cooling
system. apart from that all other points are related with
the insulation of the core,permitivity etc.
| Is This Answer Correct ? | 27 Yes | 10 No |
Answer / achala.g.s.
We can check like the following :
polarity, resistance and tap change operation tests should me made to check whether it has built correctly or not..
the ways to minimize it are:
*check of Oil quality.
*A check on the tap changer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / saravanan
oc and sc test helps to find the total losses means .oc test
gives the core loss .sc test gives the copper loss.if the
transformer is oil cooled means you must check the
conduction or breakdown test on the transformer oil. that
time only we can suggest the winding insulation loss
| Is This Answer Correct ? | 2 Yes | 7 No |
what is CRGO Transformers?
6 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd, TATA,
During Load testing of battery charger with temporary AC Generator .When reach 70% load Generator immediately shutdown .we could not able to Recognize ,what is exactly problem .Please kindly clarify us
Why do we will ground the positive terminal in electrostatic precipitator
Hello, I am just preparing my self for a university interview and struck on the 11kv ring main unit system network. I just know that ring main unit has total three breakers, fuses and use to supply a power to any load/ building without any interrupt. But i am not be able to visualize the connections, either Ring main unit getting power from two different power sources? or there is always one feeder in complete ring circuit??? I would be highly thanks full of you help me.
why auto transformer connected in star?
Which is remain unchanged in transformer action?
A 400KVA ,50HZ TRANSFORMER IS TO BE OPERATED AT 50HZ.THEN KVA RATING OF THE TRANSFORMER?.
KVAR Kilovolt-Ampere-Reactance
DIFFERNCE BETWEEN DCS AND PLC? HOW IT WORKS?
what would the resistance of a 110v 150w submersiblepump motor windings be
21. What is the purpose of taking Capacitance and Tan Delta Test in Transformer bushing? 22. What are the protections to be used for Generator? 23. Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0 24. What happens when the polarity changes in CT? Explain briefly? 25. Explain the Term in CT Name Plate – Class: 5P10
Why and which type of tertiary winding is used in most of the power transformer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)