How do we check transformer losses and what are the ways to
minimise it.
Answers were Sorted based on User's Feedback
Answer / guest
transformer losses can be found by doing open circuit test
and short circuit test
open circuit test gives the core losses
short circuit test gives the copper losses
note in open circuit test the lv side is given supply and
in short circuit test the hv side is given supply
the iron losses can be reduced by providing laminations of
thinner dimension and using c.r.g.o sheet for laminations
the copper losses depend on the winding resistance which
increases due to heat can be reduced by providing
sufficient cooling to the winding.
| Is This Answer Correct ? | 36 Yes | 2 No |
Answer / manthesh.patil
we can check transformer losses by short ckt and open ckt test
,for checking cu loss we use short ckt test and for iron
loss we use open ckt test..to reduce copper loss we should
go for good cooling and for iron loss the core should be
perfectly laminated
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / sumitgarg
we can check a trans losses by open circuit and short
sircuit test.
to minimise these losses we shuold have a good cooling
system. apart from that all other points are related with
the insulation of the core,permitivity etc.
| Is This Answer Correct ? | 27 Yes | 10 No |
Answer / achala.g.s.
We can check like the following :
polarity, resistance and tap change operation tests should me made to check whether it has built correctly or not..
the ways to minimize it are:
*check of Oil quality.
*A check on the tap changer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / saravanan
oc and sc test helps to find the total losses means .oc test
gives the core loss .sc test gives the copper loss.if the
transformer is oil cooled means you must check the
conduction or breakdown test on the transformer oil. that
time only we can suggest the winding insulation loss
| Is This Answer Correct ? | 2 Yes | 7 No |
what is different between neutral and earth?
what is the use of earthing ?
what ispositive, negative, zero sequence impedence?
If we feed 230V ac supply to a full wave rectifare, what & how much will be the out put voltage?
corona happens more in summer or winter?
Ps Explain YWY,AFWY Type Cable
Mention the disadvantages of low power factor?
How can we measure earthing resistance test (Earth meggar) of Transformer neutral pit while in live condition?.
What is difference between unity power factor wattmeter and upper power factor wattmeter? In short circuit test of transformer the wattmeter used is unity power factor type or upper power factor type wattmeter?
0 Answers Jindal Steel and Power,
1. what is difference between VCB and ACB.how its works please explian.
6 Answers ABB, Accenture, HP, Minda, Mother Dairy, Satyam Pharma,
how to calculate current when LT supply 415v fed to HT Motor 6.6kv and 1120kw.
In AC Drives How can change & control its output Frequency?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)