How do we check transformer losses and what are the ways to
minimise it.
Answers were Sorted based on User's Feedback
Answer / guest
transformer losses can be found by doing open circuit test
and short circuit test
open circuit test gives the core losses
short circuit test gives the copper losses
note in open circuit test the lv side is given supply and
in short circuit test the hv side is given supply
the iron losses can be reduced by providing laminations of
thinner dimension and using c.r.g.o sheet for laminations
the copper losses depend on the winding resistance which
increases due to heat can be reduced by providing
sufficient cooling to the winding.
| Is This Answer Correct ? | 36 Yes | 2 No |
Answer / manthesh.patil
we can check transformer losses by short ckt and open ckt test
,for checking cu loss we use short ckt test and for iron
loss we use open ckt test..to reduce copper loss we should
go for good cooling and for iron loss the core should be
perfectly laminated
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / sumitgarg
we can check a trans losses by open circuit and short
sircuit test.
to minimise these losses we shuold have a good cooling
system. apart from that all other points are related with
the insulation of the core,permitivity etc.
| Is This Answer Correct ? | 27 Yes | 10 No |
Answer / achala.g.s.
We can check like the following :
polarity, resistance and tap change operation tests should me made to check whether it has built correctly or not..
the ways to minimize it are:
*check of Oil quality.
*A check on the tap changer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / saravanan
oc and sc test helps to find the total losses means .oc test
gives the core loss .sc test gives the copper loss.if the
transformer is oil cooled means you must check the
conduction or breakdown test on the transformer oil. that
time only we can suggest the winding insulation loss
| Is This Answer Correct ? | 2 Yes | 7 No |
There are different classes of protections in power plants.class a,b,c are clear..is there any class d and e r there..and elaborate class b protection.
What are your future expectations from this company and how long do you intend to work with this company if employed?
What should be current in the Primary and secondary side of 1000KVA (11KV Supply)Transformer.?
What is the difference between synchronous asynchronous memory?
how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details three phase motor 75 kw,415 v,.85 pf,50 hz?
Why we can't start a tube light without a starter(choke) and an inductor?
why synchronous motor is not self starting
Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fault?
In the diesel generator if there is an AVR (auto voltage regulator) gone faulty, in this condition is there any way to generate the voltage from the alternator? I need a brief explanation can you please help somebody
What are the questions asked in PRDC pool campus test?(bangalore)
what is the difference between KW and KVA?
what is the procedure to carry out BDV test of a transformer ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)