3. What is Impedance Voltage in Transformer?
Answers were Sorted based on User's Feedback
Answer / sanjay sharma
it is % of rated primary voltage which require to establish
sufficient flux to produce full load current in short
circuited secondary, it is used while load loss test on
transformer.
| Is This Answer Correct ? | 6 Yes | 6 No |
Answer / hussain
Impedance voltage of a transformer is the measured voltage apply at primary winding while the secondary winding terminals of the transformer is short circuited and is increased gradually from zero till reach to full load current flows in the Primary. This voltage is much smaller than the transformer primary nominal voltage.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ahmed
Impedanc voltage value depends on the design of the transformer. decreasing this value means good transformer materials and vice versa.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / istván galamb
It is the drop (ε) of a transformer:
ε = Usc / Un x 100 = In / Isc x 100
Un = nominated primer voltage
In = nominated secunder current
USc = primer voltage to obtain the In, when the secunder
side is short cicuited
Isc = secunder short circuited current
| Is This Answer Correct ? | 6 Yes | 7 No |
Answer / ekanadam patlavath
simply is Impedance voltage of a transformer is the
voltage drop in transformer,
voltage drop in transfermer,from primary to secondry
voltage. this i called impedence voltage of transfoermer
| Is This Answer Correct ? | 21 Yes | 25 No |
two bulbs of 100w and 40w respectively connected in paralel across a 230v supply.which bulb will glow bright and why?
how to calculate the output power of vfd , please help me.
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
A 30KW motor running at 1450 rpm draws 56A, how would you determine if this is correct or not?
3 Core x 35 Sqmm Cable (How we measure 35Sqmm)
4 Answers Alpha Star, Brother,
What is the diff. between single compression and double compression gland
I WANT TO know WHICH WAY IS BETTER FOR CONNECTION BETWEEN POWER TRANSFORMER AND MAIN DISTRIBUTION PANEL. 1-IS BETTER WE USE CABLE? 2-IS BETTER WE USE BUS DUCT? my transformer rate power is 2500KVA
to improve the existing power factor whether capacitors have to be added in series or parallel.and why
In 3 phase induction motor 1hp current rating is 1.5 amps constant ? is correct or not ?
if 50hz transformer is required to be run on 50% frequency what needs to be done???????????
How can i get my certificate of competency as an electrical supervisor? I have complicated my B.Tech from Uttarakhand technical university this year (2012).
What are the types of circuit breakers ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)