Impedance voltage of a transformer is the voltage required
to
short circuit the secondary winding terminals of the
transformer and apply voltage gradually from zero at
primary winding.increase the voltage gradullay till the
full load current flows in the secondary.The voltage at
which full load current flows that voltage is the impedance
voltage of the transformer.This is required for short
circuit calculations.You can find on the transformer name
plate as Impedance voltage or percentage impedance.
| Is This Answer Correct ? | 287 Yes | 23 No |
Answer / shantanau mishra
This is the voltage required to drive full load current in a
winding of a transformer when the other winding is short
circuited.
for example if percentage impedance of a 33/11kv transformer
is 6%. it means that 33x6/100=1.98KV would be required to
drive full load current in 33kv winding when 11kv winding is
short circuited.
| Is This Answer Correct ? | 124 Yes | 19 No |
Answer / md.abul basher
impedence voltage is that voltage which is applied through
primary side and full load current is flowing in secondary
side whwnever short Ckt. of secondary side
| Is This Answer Correct ? | 107 Yes | 21 No |
Answer / manoj kumar tiwari
The percentage impedance of a transformer is the volt drop
on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage."
"It is also the percentage of the normal terminal voltage at
on side required to circulate full-load current under short
circuit conditions on other side."
The impedance of a transformer has a major effect on system
fault levels. It determines the maximum value of current
that will flow under fault conditions.
It is easy to calculate the maximum current that a
transformer can deliver under symmetrical fault conditions.
By way of example, consider a 2 MVA transformer with an
impedance of 5%. The maximum fault level available on the
secondary side is:
2 MVA x 100/5 = 40 MVA
and from this figure the equivalent primary and secondary
fault currents can be calculated.
A transformer with a lower impedance will lead to a higher
fault level (and vice versa).
The figure calculated above is a maximum. In practice, the
actual fault level will be reduced by the source impedance,
the impedance of cables and overhead lines between the
transformer and the fault, and the fault impedance itself.
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / madhu
Impedance voltage of a transformer is the voltage required
to
short circuit the secondary winding terminals of the
transformer and apply voltage gradually from zero at
primary winding.increase the voltage gradullay till the
full load current flows in the secondary.The voltage at
which full load current flows that voltage is the impedance
voltage of the transformer.This is required for short
circuit calculations.You can find on the transformer name
plate as Impedance voltage or percentage impedance
| Is This Answer Correct ? | 27 Yes | 5 No |
Answer / naufal
Simply it is the percentage of the normal terminal voltage
required to circulate full-load current under short circuit
conditions, or can also be consider as the voltage drop of
the trafo..
| Is This Answer Correct ? | 11 Yes | 7 No |
Answer / aravind kumar
Impedance voltage is calculated with short-circuit
test.which is very low compared to rated voltage. Impedance
voltage is the voltage which circulates the rated currents
when one of the two windings is shorted.
| Is This Answer Correct ? | 8 Yes | 4 No |
Answer / gopal birla
Imedance voltage is the amount of voltage required on
primary side to produce rated current on secondry side of
transformer when secondry is short circuited.
Or
amount of voltage drop accros primary side when rated
current flows through it
| Is This Answer Correct ? | 5 Yes | 5 No |
Answer / hh
Simply,if 10% means voltage drop is 10% of open cct voltage
at full load.
| Is This Answer Correct ? | 4 Yes | 4 No |
how we can varying the speed of dc motor ?
different between electrical and electronics Engineering????
why DG rating in kva
why DC motor body is plain cover but AC motor is different like finse?
Is RTCC panel needs any control supply.
What is difference between PVC cable & XLPE cable?
Dear all, I just want to ask an expert on this forum for some insights. For the magnetic balance test, when applied voltage on a Delta-Star transformer e.g. Dyn11, the following relationships apply for HV side: 1. H1-H2 = H2-H3 H3-H1 2. H2-H3 = H3-H1 H1-H2 3. H3-H1 = H1-H2 H2-H3 For the LV side also: 4. X1-X0 = X2-X0 X3-X0 5. X2-X0 = X3-X0 X1-X0 6. X3-X0 = X1-X0 X2-X0 Is there a similar pattern for Y-d, Y-Y, D-d? And how about Y-z, D-z, Z-y transformers? I've tested a YNzn5 transformer and for LV side I don't see the pattern. In this particular case I got for LV side the following (see values below): H1-H0 H2-H0 H3-H0 X0-X1 X0-X2 X0-X3 128.0 119.9 7.2 29.2 13.3 15.8 70.7 128.4 59.2 23.4 22.0 3.6 7.2 120.1 128.1 13.4 29.3 15.8 What is the relationship here for LV? For row 1 I see the relationship, for row 3 I also see but it's shifted, but for row 2 I don't see such relationship. Any suggestions, answers, someone?
WHAT HAPPENS IN DIFFERENTIAL PROTECTION IF CT REACHES ITS KNEE VOLTAGE POINT?
why the amount of voltage generated at power generating stations is 11 KV only....?
CAN 50Hz transformer work at 60 Hz power supply? if yes how it is possible?
is the value of inductance depends upon the evalue of thitha in doubly excited machine?
Is it possible to measure the voltage of a battery from a single terminal?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)