3. What is Impedance Voltage in Transformer?
Answers were Sorted based on User's Feedback
Impedance voltage of a transformer is the voltage required
to
short circuit the secondary winding terminals of the
transformer and apply voltage gradually from zero at
primary winding.increase the voltage gradullay till the
full load current flows in the secondary.The voltage at
which full load current flows that voltage is the impedance
voltage of the transformer.This is required for short
circuit calculations.You can find on the transformer name
plate as Impedance voltage or percentage impedance.
Is This Answer Correct ? | 287 Yes | 23 No |
Answer / shantanau mishra
This is the voltage required to drive full load current in a
winding of a transformer when the other winding is short
circuited.
for example if percentage impedance of a 33/11kv transformer
is 6%. it means that 33x6/100=1.98KV would be required to
drive full load current in 33kv winding when 11kv winding is
short circuited.
Is This Answer Correct ? | 123 Yes | 19 No |
Answer / md.abul basher
impedence voltage is that voltage which is applied through
primary side and full load current is flowing in secondary
side whwnever short Ckt. of secondary side
Is This Answer Correct ? | 107 Yes | 21 No |
Answer / manoj kumar tiwari
The percentage impedance of a transformer is the volt drop
on full load due to the winding resistance and leakage
reactance expressed as a percentage of the rated voltage."
"It is also the percentage of the normal terminal voltage at
on side required to circulate full-load current under short
circuit conditions on other side."
The impedance of a transformer has a major effect on system
fault levels. It determines the maximum value of current
that will flow under fault conditions.
It is easy to calculate the maximum current that a
transformer can deliver under symmetrical fault conditions.
By way of example, consider a 2 MVA transformer with an
impedance of 5%. The maximum fault level available on the
secondary side is:
2 MVA x 100/5 = 40 MVA
and from this figure the equivalent primary and secondary
fault currents can be calculated.
A transformer with a lower impedance will lead to a higher
fault level (and vice versa).
The figure calculated above is a maximum. In practice, the
actual fault level will be reduced by the source impedance,
the impedance of cables and overhead lines between the
transformer and the fault, and the fault impedance itself.
Is This Answer Correct ? | 26 Yes | 3 No |
Answer / madhu
Impedance voltage of a transformer is the voltage required
to
short circuit the secondary winding terminals of the
transformer and apply voltage gradually from zero at
primary winding.increase the voltage gradullay till the
full load current flows in the secondary.The voltage at
which full load current flows that voltage is the impedance
voltage of the transformer.This is required for short
circuit calculations.You can find on the transformer name
plate as Impedance voltage or percentage impedance
Is This Answer Correct ? | 27 Yes | 5 No |
Answer / naufal
Simply it is the percentage of the normal terminal voltage
required to circulate full-load current under short circuit
conditions, or can also be consider as the voltage drop of
the trafo..
Is This Answer Correct ? | 11 Yes | 7 No |
Answer / aravind kumar
Impedance voltage is calculated with short-circuit
test.which is very low compared to rated voltage. Impedance
voltage is the voltage which circulates the rated currents
when one of the two windings is shorted.
Is This Answer Correct ? | 8 Yes | 4 No |
Answer / gopal birla
Imedance voltage is the amount of voltage required on
primary side to produce rated current on secondry side of
transformer when secondry is short circuited.
Or
amount of voltage drop accros primary side when rated
current flows through it
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / hh
Simply,if 10% means voltage drop is 10% of open cct voltage
at full load.
Is This Answer Correct ? | 4 Yes | 4 No |
we can use airconditioner for cooling the winding of transformer ,if not why?
how will you calculate rated Primary and Secondary voltage and Current for 2500 KVA, 11kv/443V Transformer
i seen a 132kv/11kv transformer,and thier is a sugar factorys 10MW EXPORT PLANT,MY QUESTION IS THAT WHEN THEY EXPORT ELECTRICITY THEY USE THE SAME TRANSFORMER AND THE CONNECT IT TO 132/11KV TRANSFORMERS SECONDARY SIDE CAN ANY ONE EXPLAIN IT.. THE TRANSFORMER IS OF KIRLOSKAR MAKE AND IT HAS TAP CHANGER.
the electric traction poles having 3 cables n two cables touches with a insulator (or any) another one separated but it will be running 1-phase why?
Why use in ht motore
What is the method & formula of Fault level calculation in power Transformesr.
Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core
How to test IR testing & magnetic balance test
what is the difference between squirrel cage & slip ring induction motor by construction & working principle ?
What will be the effect of in HT XLPE 220 KV cable when one side of the Armour/cable ends are not grounded. Will there is difference between 3-phase voltages? like: if A. Both End of Cable grounded Phase Voltages:- V1=219 KV, v2=220 Kv, v3=220 KV. B. One End is grounded other is not: than Impact on Phase Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or unchanged??
What are the uses of lead compensator?
Difference between a pilot wire and a normal conductor?
0 Answers United Arab Aluminum Company,