Answer / pankaj rajput
It will trip on over fluxing protection, if the protection
is installed.
It's not a wise situation to connect transformer to a lower
frequency with same voltage. The flux induced in core is
directly proportional to voltage & inversly proportional to
frequency. Hence the core will be over heated/over fluxed
and may get damage due to over heat.
The only remedy is reducing the voltage in same ratio.
| Is This Answer Correct ? | 31 Yes | 2 No |
Answer / ashokreddyreguri
flux is proportional to E\f or V\f
if the frequency is reduced the ratio V\f will increase so
flux will increase.so to maintain this flux magnetizing
current required will increase.this reduces the no load
power factor , so on load power factor is also reduced.
this also reduces o\p of transformer.so V/f ratio of t/f
must be maintained constant.
as 50% of frequency is applied to maintain constant V/f
input voltage applied must be 50%if rated voltage
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / eeaadil
60 Hz is expensive to generate and safer to operate than 50 Hz
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek goyal
Xmer is the static device which can produce the voltage in
secondary side WITHOUT CHANGING OF FREQUENCY. (Pl read xmer
principle. NO CHANGE REQUIRED.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sachin_pawaskar2001
Nothing............only you will get 25hz frequency at out
put.
| Is This Answer Correct ? | 0 Yes | 24 No |
what is the question paper model for section engineer in RRB
Can a generator runs after getting 1st stator earth fault.
what gas is present in incandescent and florescent bulbs
One 15kw motor Why we used star delta feeder?why not used DOL please explain in details
3 Answers BMM Ispat, GSK, Pitti Laminations,
What is mean by sinewave.
what is meant by ceiling voltage, ceiling current?? pl reply asap
why core losses and copper losses does not depend on power factor?
In ACS 1000 drive we used 12 pulse convertor.Why dont used 6 pulse or 3 pulse convetor
whenever any squirrel or a crow falls on the transformer input line then there is a big explosion and 440 volts of power is being discharged through the neutral line due to which appliances in off mode are also burned.we have earthing for the transformer as well as the bus bar chamber.why is it happening?
can we use the 110 v primary Tr 240 v secondary step up Transformer as reverse 240 pri 110 sec
The size and construction of bushings in a transformer depend upon?
hoW to select a CT?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)