Answer / pankaj rajput
It will trip on over fluxing protection, if the protection
is installed.
It's not a wise situation to connect transformer to a lower
frequency with same voltage. The flux induced in core is
directly proportional to voltage & inversly proportional to
frequency. Hence the core will be over heated/over fluxed
and may get damage due to over heat.
The only remedy is reducing the voltage in same ratio.
| Is This Answer Correct ? | 31 Yes | 2 No |
Answer / ashokreddyreguri
flux is proportional to E\f or V\f
if the frequency is reduced the ratio V\f will increase so
flux will increase.so to maintain this flux magnetizing
current required will increase.this reduces the no load
power factor , so on load power factor is also reduced.
this also reduces o\p of transformer.so V/f ratio of t/f
must be maintained constant.
as 50% of frequency is applied to maintain constant V/f
input voltage applied must be 50%if rated voltage
| Is This Answer Correct ? | 16 Yes | 0 No |
Answer / eeaadil
60 Hz is expensive to generate and safer to operate than 50 Hz
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / abhishek goyal
Xmer is the static device which can produce the voltage in
secondary side WITHOUT CHANGING OF FREQUENCY. (Pl read xmer
principle. NO CHANGE REQUIRED.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / sachin_pawaskar2001
Nothing............only you will get 25hz frequency at out
put.
| Is This Answer Correct ? | 0 Yes | 24 No |
L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW MOTOR STARTS WITH EARTH FAULT RELEASE
why Transformer and DG rating capacity is in KVA
what is difference between multimeter and transmitter
PLC Based Process Automoation Panels?
why does the magnetic balance tests at transformers? how to provide earthing in flight?
what are the available sizes of pin type terminal lugs in the market today?
Is there any design in the world a 220 KV transformer without breather …??????
Explain What will happen when direction of field current is changed (i.e, field excitation is reversed) in the following machines? 1) Alternator 2) Synchronous Motor 3) D.C Generator ( Shunt or Seies ) 4) D.C Motor ( Shunt or Seies )
ohms law aplicable
what is difference b/w squirrel cage rotor and wound rotor
long form of CT
3 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
Can we convert off load tap changer transformer to on load tap changer transformer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)