in our 6.6kv motor feeder[it is having two sources from
Bus A&B] earth fault relay is acting, we checked CBCT
connection and cable meggerd values found very good still
earth fault acting during first two are three start after
that it will hold. please clarify what was the reason. if
same motor is starting from other Bus-A it will start.
WHAT IS THE TYPE OF 6.6KV SW.GR. hOW OLD IS THIS?
tHE EARTH FAULT RELAYS ARE VERY SENSITIVE. INSULATION
RESISTANCE OR MEGGER CAN NOT MEASURE.
CARRY OUT HV CAPACITANCE MEASUREMENT OF MOTOR,CABLE FEEDER.
AND hIGH POT TEST.
MEASURE THE TANGENT DELTA FROM DC HIGH POT.
IF MIN OIL CIRCUIT BREAKER,TEST THE OIL AND REPLACE.
WE ALSO EXPERIENCED THIS DUE TO BURNED CEREMIC/BAKELITE
PARTITION PLATES OF 6.6KV SW.GR
Is This Answer Correct ? | 0 Yes | 1 No |
whu does the power factor of diesel generator always be 0.8. please explain
How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.
Difference between online and offline UPS?
What is GIS (Gas Insulated Switchgear)
How can we calculate ac current from the given DC current when AC voltage is given?
How much should be the load percentage for 15kva Inverter and Iinut & I output load with Calculations
As load in a transformer increases, mutual flux linkage in core= A increases B decreases C not change D first increase then decrease
which type of material is used for making motor encloser
how to maintain standard votage in power system?
1)Why electric shock is feel ?? n in a Electric Train why we didnt feel that ? 2)What is the reason for transformer Noise ?? 3)What is relation b/w Transmission Lines & Communication Lines ? 4)Which material is used for making Transformer oil & How u measure its dielectric strength & Name the test ?
plz explain the snubber circuit unit
which subject is better to tell when hr asks the area of interest?..