Answer / anas
Eg3C x 35SQMM
Each core is 35SQMM (Core Red , Yellow , Blue)
To measure the conductor SQMM as per below
From BS 6360 Show that : 7/2.52mm
7/2.52mm is per below ;
Single wire diameter : 2.52mm (Based on BS 6360)
Number of Strand : 7wires (Each wire is 2.52mm)
Calculation
=(2.52mm)(2.52mm) x PI()/4 x Number of Wire (7)
= 34.9131 approximate 35SQMM
Is This Answer Correct ? | 47 Yes | 14 No |
Answer / p. h. godavary
Cable size (area of each core) is normally specified in square millimeters
(sq. mm). In this case it is 35 sq. mm. The cable size is always printed / marked on the cable itself by the manufacturer.
The conductor in each core of power cables is normally made of multi strand circular wires (Copper / Aluminum ).
To measure the size/area of the conductor, measure the diameter of a strand in a core and calculate its area. Multiply this area by number of strands in a core.
If the diameter of a strand in mm is D,
then its Area = [∏/4] [ DxD ] = [3.14/4 ] [DxD] Sq. mm.
Size of the cable (or) Cross sectional Area of a Core
= [Area of a strand x No. of strands in the core].
Is This Answer Correct ? | 33 Yes | 9 No |
Answer / p.h.godavary
In my answer (Answer #2), I have used the Phi symbol in the 'Area Formula'. But I find the same is appearing scrambled.
Is This Answer Correct ? | 5 Yes | 5 No |
Answer / ali
you are measure the one conductor size 35 sqmm cable in
micro meter than you give a size in squre and multiple by
pae multiple by number of conductor dividing by number of
core,you are give the any cable size.
for example. i measure the 4 core * 300 sqmm cable size
(2.5)squre x pae x 61 /dividing by number of core 4
you have size the cable
Is This Answer Correct ? | 17 Yes | 21 No |
why fuse amperes rating are specified ratings like 32amp & 64 amps?
what is the difference between vector scale and vector diagram?
I have 200 KVA Isolation Transformer for UPS input side. & ups was having 48% load, suddenly got short what will be the reason.
In response to Mr Bikas. If fault current is 52 kA then what will be the CT specification
SMPS (Switch Mode Power Supply) unit is denoted by KW or KVA?
if the magnetic lines can pass through a vaccuum area
What happens on the secondary of a 33kV/11kV when one phase of the primary fuse blows?
why is corona loss greater in a stranded conductor as compared to a solid conductor ?
2 electric bulbs of 100w,200V are put in series & the combination of each bulb is supplied to 100 V . the power consumption of each bulb will be????????
explain types of electric welding and its applications
What is EHT(Abrebiation,Function,Voltage Regulation & how it works?
what is metering cum synchronizing panel and how it is used?