Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why the generator rating in kva

Answers were Sorted based on User's Feedback



Why the generator rating in kva..

Answer / yajnesh

The rating of generator is described in terms of KVA by the
manufacturer because he does not know the nature of load,
that the consumer will put on it.
While in case of motor,motor have fixed power factor

Is This Answer Correct ?    3 Yes 2 No

Why the generator rating in kva..

Answer / hiren

bcz the output in kw. is dependent on p.f. and kva o/p.
independent of p.f.for example asingle phase alternator
drawing 50 amp atunity p.f. at 230v has an o/p. of
(50*230)=11.5kw at unity p.f: (50*230*0.6)=9.6kw.at
0.8 p.f.and (50*230*0.6)=9.6kwat 0.6 p.f. but the kva
rating of alternator is (230*50)=11.5kva.

Is This Answer Correct ?    1 Yes 0 No

Why the generator rating in kva..

Answer / shahid siddique

As generator may be connected to any type of load(Inductive,Capacitive) therefore primarily it is independent of power factor,so we rating of generator which produces voltage and currents(v*i) is rated in kva, as motors have specific load nature (mostly inductive having specific power factor) are rated in kw

Is This Answer Correct ?    1 Yes 0 No

Why the generator rating in kva..

Answer / vishnu

in transformer, two type of losses present 1. copper losses ans 2. core losses
copper losses(I*I*R) depend upon current I(amp)
and core losses ((v*v)/R) depend upon voltage (volt)
so as a result the rating of transformer is KVA.....

Is This Answer Correct ?    1 Yes 0 No

Why the generator rating in kva..

Answer / ranvijay

Generator is producer of Voltage and Current, we can
connect load as such draining full load current or half
load, even noload,but voltage remain moreover same.So it
willl rated in terms of product of V*I, secondly it gives a
electrical output for any Load(may Capacitor,Inductor &
resistor),so it is consider as Procuct of Voltage & Current
excluding powerfactor.
Whereas motor is machines coverts electrical Energy to
Mechanical energy, so it is rated

Is This Answer Correct ?    0 Yes 0 No

Why the generator rating in kva..

Answer / srujana

generator delivers the power ,it includes only voltage& current simply.but motor gail the power and it gives the mechanical energy,it includes the power losses also.thats why motor rating in KW.and generator rating in KVA.

Is This Answer Correct ?    0 Yes 0 No

Why the generator rating in kva..

Answer / baskar

Generator is the equipment where the voltage & current starts their journey SIMULTANEOUSLY. Hence no question of Power Factor coming in. Hence it is termed in KVA(V*I)

But Motor is the destination any power generated , after completing its journey thru an Impedance path , where the "Sync" between Voltage & Current is lost due to line impedance.
Hence the factor Power factor arises , due to displaced Voltage& current .Hence it is termed in KW (V*I*Cos phi)

Is This Answer Correct ?    0 Yes 0 No

Why the generator rating in kva..

Answer / rahul

the kva is apparent power here E and I are taken into
account but kw is real or true power here an addition power
factor is taken so VA=E*I
KW=E*I*power factor

Is This Answer Correct ?    0 Yes 0 No

Why the generator rating in kva..

Answer / essien ifiok (university of po

We all know that Transformers are rated in kVA, Generator and Alternator rated in kVA as well. Designers do not know the actual consumer power factor while manufacturing transformers and generators i.e. the P.F (Power factor) of Transformer and Generator/Alternator depends on the nature of connected loads either resistive load, capacitive load, or inductive load as Motors. All these are the apparent power where the power factor is defendant of the connected load.

Is This Answer Correct ?    0 Yes 0 No

Why the generator rating in kva..

Answer / vijendra kumar bairwa

The power √3 VL IL Cos φ delivered by the alternator for the same value of current, depends upon p.f. (Power Factor=Cos φ) of the load. But the alternator conductors are calculated for a definite current and the insulation at magnetic system are designed for a definite voltage independent of p.f. (Cos φ) of the load. For this reason apparent power measured in kVA is regarded as the rated power of the alternator.
Why alternator rated in kVA.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Does the total power means fundamental plus Harmonics?

2 Answers  


Can any one give an explanation about rating factors of cable? if we are laying the cable on the air with an temp 15 degree then rating factors will be 1.15 and if we are laying the cable on the air an temp 60 degree then rating factor will be 0.76 please describe it and what is the difference between rating factor and derating factor?

0 Answers  


what is the difference between NC & CNC machine.what is the difference between equipment & machine tool

2 Answers  


Where the Dry type tranformers are used.

5 Answers  


While miss missed name platform fo electric motor how to calculate simple fourmul,?

1 Answers   ABB, ABC,


what is mean by D.O. in distribution line poles?

0 Answers  


how the magnetic flux is said to be rotating & alternating?

4 Answers  


What is given by the definition in BIL IMP/PF = 950/395 kV. This was found in a name plate of a power transformer.

0 Answers   AES,


in the case of 6.6kv motor starter combination contain fuses on it VCB. but in 11KV motor starter combination Fuses are not using in it's VCB why?

0 Answers  


Define what is power quality meter ?

0 Answers  


What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.

0 Answers   TATA,


why we use post insulators in no ofstacks at substation for supporting equipment ? why we not use single post insulator

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)