why we use REF and Differential Protection in one
transformers?my doubt is both protections are operated in
internal fault only.why we want to use 2 protections?please
clarify.
Answers were Sorted based on User's Feedback
Answer / ramji
The differential protection is used for protecting the
transformer from internal winding fault,internal winding
shorts etc.,.It operates through three sets of CT's
connected in and out of transformer.It may or may not
operate during minor earth faults.REF is used to detect the
earth fault at restricted zone where its protection CT is
connected.It will surely operate during earth fault.But not
in windings short.
| Is This Answer Correct ? | 31 Yes | 4 No |
Answer / gunasekaran
both are using for internal fault but differential
protection only sensitive up to 92% winding of the
transformer if any fault occur in balance 8% winding diff is
not operating so we r using REF protection
| Is This Answer Correct ? | 11 Yes | 7 No |
Answer / nikhil thakkar
REF and Differential both pritection are for internal zone and SEF for external zone. Actual all protections are voltage/current/power based and they are back to each other. DIFFERENTIAL AND REF both protection is for internal fault i.e trafo winding . differential sense unbalance between both end of trafo. /Gen. . REF sense unbalance caused between NCT and phase CTdue to earth fault abd actual backup for REF is SEF.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ashish
as per my knowledge ref protections hav to be assigned
separately on both sides of traffo it protects 90% of
winding.
it is unit protection and its very sensitive.
while talking about diff protection two cts in each phase
on both sides of trafo is there any diff in incoming and
outgoing current will leads to trip so both are equally
required.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / raveendra nath
Differential protection provides excellent protection for
phase- to-phase and most phase - to - earth faults, this
element is less sensitive for single- phase-to-earth faults
close to the earth point in solidly earthed transformers.
For these faults (i.e fault at transformer winding turns
nearer to neutral point ), phase current changes very
little, but large current flows in the neutral.
| Is This Answer Correct ? | 3 Yes | 5 No |
Answer / gunasekaran
at internal earth fault condition diffrentional sensitive
only 85% only remaining 15% covered by REF protection
| Is This Answer Correct ? | 1 Yes | 8 No |
Answer / munish
REF 64T is used for protect the 95% winding of T/F.it sens
only the internal fault of T/F and 51NT circulating earth
fault relay used for detect the other area.
87T diff. is act only when the difference B/W both side
current is more than setting value
| Is This Answer Correct ? | 0 Yes | 8 No |
why frequency meter is connected in parallel in a circuit?
1 Answers University of Engineering and Technology,
when i am going to take trail on a 3ph sq.i/m motor 5.5kw, i observed that RPM of the motor is very low as compared to the rated RPM and also it rotates in clockwise in first ON command,and anticlock wise in second ON command. finally i observed that on phase is no available . but iam not clear about, why the motor is rotates in both directions without any phase interchanging.pls answer to my question.
What is resonant peak?
wheather the size of windings in motor and generator are the same
Why field resistance is greater than the armature resistance in dc mechine
1 Answers Cape Peninsula University of Technology,
is it possible to step down voltage of single phase from a three phase sysem? explain
what is the significance of KV & MVA rating of the transformer and how they are related.
How to calculate the efficiency of Turbo Generator(Alternator) in general....?
how a flip flop can be used as a latch?
What is IDMT relay how it works.
3 Answers Electrotherm, Sulzer,
Mention what are the different colors on wires indicates?
what is the safety of ACB & VCB and how can this work and how can the service the ACB & VCB parts name with picture
21 Answers ABB, ACB, Bharti, Claris Lifesciences, Honda, L&T, RotoPower, Sterling Wilson, Wipro,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)