What is the formula for finding fault level of generator?
Answers were Sorted based on User's Feedback
Answer / ramesh
I would like to answer by way of an example:
Generator capacity = 12MVA
Generator sub-transient impedance = 12%
With above two data,
the generator fault level can be calculated as folows:
Generator fault level = Generator capacity / generator sub-
transient impedance
Generator fault level = 12 MVA / 12% = 12MVA/.12 = 100MVA
To get fault current = Generator fault MVA / (1.732 *
generator rated voltage)
In case of single phase generator 1.732 to be ignored.
| Is This Answer Correct ? | 49 Yes | 4 No |
Answer / ramesh
From your question I guess there is transformer between the
11kV & 6.6kV you are refering to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / dhiren patel
what is the refected current in 6.6 KV system in case of 11
kv side fault current is 40 KA and 8000 A full load current.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / mnaoj sharma
Ramesh whats ur Email ID .I want to know more about you. I
mam electrical engineer . Your answers are absolutely right.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / jignesh
we have 3 sets of generator running in parallel gen data 11kv 2000kva 1600kw transient reactance 0.1772and sub transient 0.1998 NGR 63.2 ohm . What is the fault level and fault current ? Please give me the solution on my mail id
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
RAMESH WTS UR EMAIL ID.....SEND ME UR EMAIL ID AT MY ID ...MY ID IS vinodmemoria07@gmail.com
i need ur help plz 4ward
| Is This Answer Correct ? | 0 Yes | 1 No |
From your question I guess there is transformer between the
11kV & 6.6kV you are referring to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
mail-behera.ramesh@orisysinfotech.com
| Is This Answer Correct ? | 0 Yes | 1 No |
Why air gap in rotating machines should be small?
How the speed of synchronous motor changes with the variation of load?
What is the meaning of ST and HT in electrical transmission and what are thier range.
difference between Ac and Dc mcb ????
working principles of a generator
sir iam a 3rd yr eee student.no core company comes for recruitment to our college.my aim is to be placed in l and t.tell me the procedures.
Can we connect two or more energy meters/Amp meters on one CT set(Three phase).
5 Answers Parle, Watermark Engineering,
What are the tests to be taken on a transformer and generator?
What is main cause of cable's terminal point burned in Lug on high temperature although lug and cable selection is ok as per stantard and also tightness is ok as per situation. so please take in deep and tell correct answer thanku.
Sir i completed diploma in electrical from govt. Polytechnic dhanbad (jharkhand) . In 2012 . Now i am working in sail iisco plant . Sir i want to get electrical supervisory certificate for applying in ongc . From where i get this certificate please guide me procedure step by step
motor is 12.5hp after starting few minets motot get hot? why?
what are types of ups?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)