What is the formula for finding fault level of generator?
Answers were Sorted based on User's Feedback
Answer / ramesh
I would like to answer by way of an example:
Generator capacity = 12MVA
Generator sub-transient impedance = 12%
With above two data,
the generator fault level can be calculated as folows:
Generator fault level = Generator capacity / generator sub-
transient impedance
Generator fault level = 12 MVA / 12% = 12MVA/.12 = 100MVA
To get fault current = Generator fault MVA / (1.732 *
generator rated voltage)
In case of single phase generator 1.732 to be ignored.
Is This Answer Correct ? | 49 Yes | 4 No |
Answer / ramesh
From your question I guess there is transformer between the
11kV & 6.6kV you are refering to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / dhiren patel
what is the refected current in 6.6 KV system in case of 11
kv side fault current is 40 KA and 8000 A full load current.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / mnaoj sharma
Ramesh whats ur Email ID .I want to know more about you. I
mam electrical engineer . Your answers are absolutely right.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / jignesh
we have 3 sets of generator running in parallel gen data 11kv 2000kva 1600kw transient reactance 0.1772and sub transient 0.1998 NGR 63.2 ohm . What is the fault level and fault current ? Please give me the solution on my mail id
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
RAMESH WTS UR EMAIL ID.....SEND ME UR EMAIL ID AT MY ID ...MY ID IS vinodmemoria07@gmail.com
i need ur help plz 4ward
Is This Answer Correct ? | 0 Yes | 1 No |
From your question I guess there is transformer between the
11kV & 6.6kV you are referring to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
mail-behera.ramesh@orisysinfotech.com
Is This Answer Correct ? | 0 Yes | 1 No |
What happens to the synchronous generator when reverse power is given to it?
how to calculate full load current of transformer & induction moter ?
Differnce between Analog & Digital
I have 150/1A Rating CT Suppose if i inject 15A in CT " Secondary" means what will happen ??????
how can we find a burden of potential transformer? what does it effects? how can we calculate rated load of it?
Whether amorphous core transformer is commercialized or not:Name of company making amorphous core transformer and what are different rating?
In AC Drives How can change & control its output Frequency?
what will happen to give a dc supply in transformers?
IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL. AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE PROVIDED
how will calculate the safe starting current of 3-phase squirrel cage induction motor?
after how many spot we must chang secondry cable in portable spot welding gun?
what are the main hormonics in ac?