Answer / ramesh
I would like to answer by way of an example:
Generator capacity = 12MVA
Generator sub-transient impedance = 12%
With above two data,
the generator fault level can be calculated as folows:
Generator fault level = Generator capacity / generator sub-
transient impedance
Generator fault level = 12 MVA / 12% = 12MVA/.12 = 100MVA
To get fault current = Generator fault MVA / (1.732 *
generator rated voltage)
In case of single phase generator 1.732 to be ignored.
| Is This Answer Correct ? | 49 Yes | 4 No |
Answer / ramesh
From your question I guess there is transformer between the
11kV & 6.6kV you are refering to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / dhiren patel
what is the refected current in 6.6 KV system in case of 11
kv side fault current is 40 KA and 8000 A full load current.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / mnaoj sharma
Ramesh whats ur Email ID .I want to know more about you. I
mam electrical engineer . Your answers are absolutely right.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / jignesh
we have 3 sets of generator running in parallel gen data 11kv 2000kva 1600kw transient reactance 0.1772and sub transient 0.1998 NGR 63.2 ohm . What is the fault level and fault current ? Please give me the solution on my mail id
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod
RAMESH WTS UR EMAIL ID.....SEND ME UR EMAIL ID AT MY ID ...MY ID IS vinodmemoria07@gmail.com
i need ur help plz 4ward
| Is This Answer Correct ? | 0 Yes | 1 No |
From your question I guess there is transformer between the
11kV & 6.6kV you are referring to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further
mail-behera.ramesh@orisysinfotech.com
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the advantage and disadvantage of billing in kwh and kvah by electricity board .
what is meant by residual over voltage & residual earth fault ?
How to maintain ac plant?
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
What is the voltage violating limit to be considered for load flow study? What is acceptable deviation limit according to relevant standards?
Explain the method to keep noises low in a control system?
why does a dc machine has high efficiency while working as a generator than as a motor ..
How to size the Neutral grounding resistor?
how to calculate the cable current ratingand and how much of distance the rating will be ok will the distance is incresed what the action we take
A 3-phase IM is supplied from 50 Hz system. It runs at speed of 1440 rpm and slip equal to 4 %. Calculate number of pole pairs. A 1 B 6 C 2 D 3
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
what is the meaning of bus bar, in electrical panels.
13 Answers HLG Habtoor Leighton Group,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)