What is the formula for finding fault level of generator?

Answers were Sorted based on User's Feedback



What is the formula for finding fault level of generator?..

Answer / ramesh

I would like to answer by way of an example:

Generator capacity = 12MVA
Generator sub-transient impedance = 12%

With above two data,
the generator fault level can be calculated as folows:
Generator fault level = Generator capacity / generator sub-
transient impedance

Generator fault level = 12 MVA / 12% = 12MVA/.12 = 100MVA

To get fault current = Generator fault MVA / (1.732 *
generator rated voltage)

In case of single phase generator 1.732 to be ignored.

Is This Answer Correct ?    49 Yes 4 No

What is the formula for finding fault level of generator?..

Answer / ramesh

The simplest formula is geno MVA / geno Xd".

Is This Answer Correct ?    27 Yes 6 No

What is the formula for finding fault level of generator?..

Answer / ramesh

From your question I guess there is transformer between the
11kV & 6.6kV you are refering to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further

Is This Answer Correct ?    6 Yes 0 No

What is the formula for finding fault level of generator?..

Answer / shaan

Could u tell me what s mean by geno MVA/geno xd

Is This Answer Correct ?    10 Yes 5 No

What is the formula for finding fault level of generator?..

Answer / dhiren patel

what is the refected current in 6.6 KV system in case of 11
kv side fault current is 40 KA and 8000 A full load current.

Is This Answer Correct ?    5 Yes 1 No

What is the formula for finding fault level of generator?..

Answer / mnaoj sharma

Ramesh whats ur Email ID .I want to know more about you. I
mam electrical engineer . Your answers are absolutely right.

Is This Answer Correct ?    4 Yes 1 No

What is the formula for finding fault level of generator?..

Answer / arun

Thanks Mr. Ramesh
from Arun Sharma
ENERGY AUDITOR

Is This Answer Correct ?    2 Yes 2 No

What is the formula for finding fault level of generator?..

Answer / jignesh

we have 3 sets of generator running in parallel gen data 11kv 2000kva 1600kw transient reactance 0.1772and sub transient 0.1998 NGR 63.2 ohm . What is the fault level and fault current ? Please give me the solution on my mail id

Is This Answer Correct ?    0 Yes 0 No

What is the formula for finding fault level of generator?..

Answer / vinod

RAMESH WTS UR EMAIL ID.....SEND ME UR EMAIL ID AT MY ID ...MY ID IS vinodmemoria07@gmail.com
i need ur help plz 4ward

Is This Answer Correct ?    0 Yes 1 No

What is the formula for finding fault level of generator?..

Answer / ramesh

From your question I guess there is transformer between the
11kV & 6.6kV you are referring to. We need the transformer
MVA and the impedance percentage.
Once your provide the transformer MVA and its %impedance I
can answer further


mail-behera.ramesh@orisysinfotech.com

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

What happens to the synchronous generator when reverse power is given to it?

1 Answers  


how to calculate full load current of transformer & induction moter ?

2 Answers  


Differnce between Analog & Digital

1 Answers  


I have 150/1A Rating CT Suppose if i inject 15A in CT " Secondary" means what will happen ??????

1 Answers  


how can we find a burden of potential transformer? what does it effects? how can we calculate rated load of it?

4 Answers   Areva, KPTCL,






Whether amorphous core transformer is commercialized or not:Name of company making amorphous core transformer and what are different rating?

0 Answers   DAE,


In AC Drives How can change & control its output Frequency?

5 Answers   Jindal,


what will happen to give a dc supply in transformers?

3 Answers  


IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL. AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE PROVIDED

2 Answers   BSF,


how will calculate the safe starting current of 3-phase squirrel cage induction motor?

0 Answers  


after how many spot we must chang secondry cable in portable spot welding gun?

0 Answers  


what are the main hormonics in ac?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)