What is the voltage violating limit to be considered for
load flow study? What is acceptable deviation limit
according to relevant standards?
Answer / omar aziz
Mostly standards (IEEE , ANSI) recommend 5% however, in
practical situations where a sound judgment can be made you
can strech it upto 10 - 15% at the load bus depending on
your min. voltage allowed by the motors/ other equipment.
Motors can usually start at around 80% rated voltage ,
however other electronic equipment such as UPSs are very
sensitive to voltage variations.
Consider the load before selecting this threshold otherwise
stick to 5%
| Is This Answer Correct ? | 1 Yes | 0 No |
What is the material used for the core of a high freiquency transformer?
what solid earthing means?
can u describe the method used for protection of transmission line.
The reason why the sending end and receiving end voltage sare almost equal when capacitive load is added.
Which type starter is used for synchronous motor?
How does a television work?
how capacitor can split the phase.
What happen while we measure the Current in Rotor?
What is I to C?
what about GD square and its important for motor design?
what will be happen if we apply D.C supply to the transformer
Why Two Transformers aside shoud be supperated by concreted wall?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)