Answer / nagarajan
For example 20/25MVA Power Trans -132/6.9kv
1. FLC of Secondary=2092A
2.Phase to Phase Voltage for Secondary=6.9/1.732=3.98Kv
3.NGR =3980/2092=V/I=1.90Ohms for 30sec
It is only for power transformer.
| Is This Answer Correct ? | 2 Yes | 1 No |
kindly tell me how the load on generator increase by just increasing the fuel of prime mover, as if for exampple 20 MW gen set is synchronized the load ramps from zero to 20 MW gradully and during this procress only fuel of prime mover increases. Which thing determines the load on generator with respect to fuel
What is the different between feeder & bus?
what is purpose of using neutral grounding transformer in generators??
How to find the maximum load(in KW)in a big industry, having motors,lights,lifts etc..?
230v 1 phase Phase and Neutral insert in Bulk water what happens.
what is electricial and mechnical interlock.
9 Answers Control Dynamics, EFS, HP,
current and voltage equations for a star connected load fed from a delta connected load.
why HT motors are earthed only at equipment side & for it's single core cable with aluminium wire armoure using?
1 Answers Legrand, NLC Neyveli Lignite Corporation Limited,
what is the IPC ? & what the uses ?
What are options used for earthing the switchgear.
Whot is the difference between MCB and MCCB.Whot is the selection critearea for MCCB and MCB for 63 Amp.
Whats the use of earth pits? and it will function? whats the natural earth value? How to improve ur earth resistance?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)