How to take Vector group test of Transformer?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2,3) the vector group of transformer is
verified
| Is This Answer Correct ? | 225 Yes | 28 No |
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W2N- Which is secondary-Star connection
3.By connecting terminals 1U& 2U
4.Then three phase Supply is given to 1U-1V-1W
5.By measuring the terminal given below
We get
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
THE BELOW GIVEN CONDITION IS SATISFIED THEN DYn11 IS
CONFIRMED
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
| Is This Answer Correct ? | 121 Yes | 26 No |
Answer / vinod
Vector group is punched on the name plate based on the user
requirement by the manufacture. Aim of vector group test is
at site is to check if their is any damage in the windings
during transportation and erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted for all vector group of transformer
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / srinivas
can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz
| Is This Answer Correct ? | 18 Yes | 8 No |
Answer / adi
Procedure given by Mr. dinesh kumar & Mr. E.saravanan is
correct but is there any explanation for this three
conditions.
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / prasad talada
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / vinay kumar
can anybody tell hw u r writing this is the vector group
calculation for this one.....
what happens if the voltages r not satisfied for the
specified vector group and if so what to do.......
| Is This Answer Correct ? | 7 Yes | 3 No |
what is the function of step up transformer?
What is the significance of vector grouping in Power Transformers??
what is infinite in infinite bus
anyone knows service engineer in chennai for EDM SPARKING MACHINE.CHMER PULSE CD 60 M.pL GIVE ANY CONTACT NOS
how we calculate electricity unit ( meter unit.. for knowing how many charges) from on motor load.?
Differentiate between ideal and non ideal current sources?
Is RTCC panel needs any control supply.
How to parallel a alternator without using synchro scope or lamp methods
Why Magnetic Core Balance test is performed only on Star side of Transformer and not on Delta Side of Transformer (Vector Group Dyn11)?
What is Single Phasing fault???(not single-phase fault)
could anyone suggest project title
Why is DC use instead of AC for protection and control circuits?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)