How to take Vector group test of Transformer?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2,3) the vector group of transformer is
verified
Is This Answer Correct ? | 225 Yes | 28 No |
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W2N- Which is secondary-Star connection
3.By connecting terminals 1U& 2U
4.Then three phase Supply is given to 1U-1V-1W
5.By measuring the terminal given below
We get
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
THE BELOW GIVEN CONDITION IS SATISFIED THEN DYn11 IS
CONFIRMED
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
Is This Answer Correct ? | 121 Yes | 26 No |
Answer / vinod
Vector group is punched on the name plate based on the user
requirement by the manufacture. Aim of vector group test is
at site is to check if their is any damage in the windings
during transportation and erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted for all vector group of transformer
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
Is This Answer Correct ? | 19 Yes | 5 No |
Answer / srinivas
can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz
Is This Answer Correct ? | 18 Yes | 8 No |
Answer / adi
Procedure given by Mr. dinesh kumar & Mr. E.saravanan is
correct but is there any explanation for this three
conditions.
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
Is This Answer Correct ? | 13 Yes | 3 No |
Answer / prasad talada
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / vinay kumar
can anybody tell hw u r writing this is the vector group
calculation for this one.....
what happens if the voltages r not satisfied for the
specified vector group and if so what to do.......
Is This Answer Correct ? | 7 Yes | 3 No |
What is the difference between grid and off- grid system??
what is the principle to generate energy from water or coal, plz define the step by step how & when electricity energy start from resource area to ours home meter & separate & how meter read the voltage or current?
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
Shall we use Dyn1 transformer in place of Dyn11 for motor application as a distribution transformer
what is broken conductor indication
why, when birds sit on transmission lines or current wires doesn't get shock?
36 Answers College School Exams Tests, Infosys,
WHAT IS THE FUNCTION OF PULSE TRANSFORMER IN DC DRIVE
how to calculate voltage drop in long distance cable? for an e.g lamp of 12 volt ac ,300watt is 90 meter away from supply i.e (x'mer 230 v / 12v)and i m getting 8 volts at lamp terminal ....
some ac motor's direction get change dueto ghanging input to the ac drives.(say ryb to rby). but some motor direction remains the same when phase sequence is changed fromdive side. can anybody guide me?
What happens when the power factor is leading and its disadvantages.
what is advertised hop count
what is PWM in IGBT and how it works for drive.?