How to take Vector group test of Transformer?
Answers were Sorted based on User's Feedback
Answer / dinesh kumar
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2,3) the vector group of transformer is
verified
| Is This Answer Correct ? | 225 Yes | 28 No |
Assumed the transformer vector group is DYn11;
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W2N- Which is secondary-Star connection
3.By connecting terminals 1U& 2U
4.Then three phase Supply is given to 1U-1V-1W
5.By measuring the terminal given below
We get
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
THE BELOW GIVEN CONDITION IS SATISFIED THEN DYn11 IS
CONFIRMED
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
| Is This Answer Correct ? | 121 Yes | 26 No |
Answer / vinod
Vector group is punched on the name plate based on the user
requirement by the manufacture. Aim of vector group test is
at site is to check if their is any damage in the windings
during transportation and erection.
3 -phase AC supply is given on HV side. R-Phase HV and r-
phase LV shorted for all vector group of transformer
Then to qualify the test following conditions are to be
satisfied after measurement of voltages.
nR+nY=RY, By>> Bb and Yb=Yy.
| Is This Answer Correct ? | 19 Yes | 5 No |
Answer / srinivas
can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz
| Is This Answer Correct ? | 18 Yes | 8 No |
Answer / adi
Procedure given by Mr. dinesh kumar & Mr. E.saravanan is
correct but is there any explanation for this three
conditions.
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
| Is This Answer Correct ? | 13 Yes | 3 No |
Answer / prasad talada
1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / vinay kumar
can anybody tell hw u r writing this is the vector group
calculation for this one.....
what happens if the voltages r not satisfied for the
specified vector group and if so what to do.......
| Is This Answer Correct ? | 7 Yes | 3 No |
how harmonics are generated due to nonlinear load & how harmonic filters work?
what is non uniform load
Define the three phase formula fuse.
how to identify 3phase....r y b .A new make altnator how to identify R
In Ferantti Effect Receiving end voltage is greater than sending end voltage but how it is possible. I know its all about charging current but give me some more detailed explaination?
How would you supply power to a village which is very far from a sub-station and has only a 11kV line running near by?
explain supply side and demand side energy management with advantages & disadvantages
how system fault level is calculated?
What_is_mean_by_negative_dc_voltage? why we use -48v except +48v in DC power supply systems.
What is the difference btwn grounding and earthing?
A motor works on 30kw.it is working on 440volts.How much amper will be Required?
State kirchoff current law?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)