How to take Vector group test of Transformer?
Answers were Sorted based on User's Feedback
Answer / ambrish
Pl. show the standard formula to check vector group tst for
any type of transformer.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tansford
Superimpose the HV & LV vectors with 1U & 2U as common it
clearly shows the relation between the phasors
Every vector group will have a different relation &
equation to be evaluated
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raj_singh_0376
Procedure of vector group test of transformer
Let’s have a YNd11 transformer.
1) Connect neutral point of star connected winding with earth.
2) Join 1U of HV and 2W of LV together.
3) Apply 415V, three phase supply to HV terminals.
4) Measure voltages between terminals 2U – 1N, 2V – 1N, 2W – 1N, that means voltages between each LV terminal and HV neutral.
5) Also measure voltages between terminals 2V – 1V, 2W – 1W and 2V – 1W.
For YNd11 transformer, we will find,
2U – 1N > 2V – 1N > 2W – 1N
2V – 1W > 2V – 1V or 2W – 1W
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / ponnudura
can anyone say me hoe to draw vector group and what is the
use of different vector group and its application plz
Is This Answer Correct ? 17 Yes 8 No submit
srinivas
Answer
# 8 1.1U1V1W-which is primary -Delta Connection
2.2U2V2W- Which is secondary-Star connection
3.join 1U& 2U terminals
4.Supply 1U-1V-1W 440v Measured
a.1U-1V
b.1V-1w
c.1W-1U
d.1W-2W
e.1V-2W
f.1V-2V
g.1W-2V
h.1U-2N
i.1V-2N
TO CHECK
1.1V-2W=1V-2V
2.1W-2V>1W-2W
3.1U-1V=1V-2N+1U-2N
From above check(1,2) the vector group of transformer is
verified
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balaji
1) Can i know why we are making short of any phase during vector group test ?
for Example R-r,Y-y Like that
2) while doing the vector group why the neutral earth should be removed ?
| Is This Answer Correct ? | 0 Yes | 0 No |
WHY WE USE 4-20mA
What are the causes of electrical faults?
how can check the resistance of battery contact?
1.why motor rating in kw instead of KVA? 2.why alternators rating in KVA instead of KW?. 3.why transformer rating in KVA instead of KW?.
why overload relay is not tripped at time of starting of motor allthough staring current is too high?
What does Bode plot tell you?
which calss ct's,pt', use protection,meatering and others
IF ANY MATERIAL AVAILABLE IN MARKET FOR MOTOR PROTECTION INSTEAD OF OLR & CONTACTOR ?
As per standard, transformer body earthing and other Equipment earthing (Equipment earthing) did not connect. but in LT side termination we are doing metal glanding in both side Transformer to PCC Panel through armoured cable, now X'mer body earthing and PCC Pane earthing (Equipment earthing) both are connect.is this safe for X'mer or other equipment?
No load test of induction motor is carried out to compute= A stator resistance B rotor resistance C magnetizing reactance D rotor reactance
what is mean by dry frequency
why are laminations used in constructing the field core?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)