In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?
Answers were Sorted based on User's Feedback
Answer / pillay
your transformer had become a step up transformer for some
hours, if you have not connected any load to it than there
is no damage to your load.your transformer itself would not
have undergone any damage and safe to use.Please inform us
what actually happened.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / girish naik
The transformer secondary is designed for 220V..Its having
lesser turns than 415V side..so if we apply 415V it
experiences overfluxing and damages the insulation losses
and also the temparature..
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / pillay
this is a case of a stepdown transformer being used as
step up transformer.
as mr milan has said 816.12 would be at the other side.
generally nothing would have happened to the transformer
other than being warm.the transformers insulation class
would be able to take care of the higher voltage.
If the other side the 816.12 volt have been connected to
the
load (suppose to be 200 volts)than damage would have
happened
to the load, the extent depending on what type of
load.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / manjeet kumar
if u connect 415 secondary side for some hour your load not
operate and transformer secondary side is damage.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / sanket patil
First of all primary and secondary of a transformer are
decided after putting it in the service. Hence the windings
of transformer are referred as HV and Lv windings.
Now if the HV winding is connected as a secondary then
the xmer will work satisfactorily
In the another case if 220V wdg is connected to the 415V
supply the answer is same as explained by other friends.
| Is This Answer Correct ? | 2 Yes | 6 No |
Answer / maan
Most of electrical equipment are rated at 220v,there
working seriously affected if they recive power at haigher
voltage(415v), also losses in primery side increases and
core loss in secondary side , that may damage winding and
insulation.
| Is This Answer Correct ? | 1 Yes | 9 No |
what is difference between multimeter and transmitter
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?
CORRECT INFORMATION ABOUT TRANSFORMERS,what actually transformer is?
how to modify DOL control panel into Delta Y connection?
what happen when dc supply is given to the transformer
How power cable & control cable can be differentiate from each other ?explain?
14 Answers Aster, Finolex, TCE,
Why AC loads wont used in DC input supply? and Why DC loads wont used in AC input supply?
for what purpose the star point is done in ct
how to work exciter in 10 MW alternator?
What is DC power factor??
What are the tests to be conducted in the electrical installations
why the transformer ratings in kva
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)