In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?
Answers were Sorted based on User's Feedback
Answer / pillay
your transformer had become a step up transformer for some
hours, if you have not connected any load to it than there
is no damage to your load.your transformer itself would not
have undergone any damage and safe to use.Please inform us
what actually happened.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / girish naik
The transformer secondary is designed for 220V..Its having
lesser turns than 415V side..so if we apply 415V it
experiences overfluxing and damages the insulation losses
and also the temparature..
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / pillay
this is a case of a stepdown transformer being used as
step up transformer.
as mr milan has said 816.12 would be at the other side.
generally nothing would have happened to the transformer
other than being warm.the transformers insulation class
would be able to take care of the higher voltage.
If the other side the 816.12 volt have been connected to
the
load (suppose to be 200 volts)than damage would have
happened
to the load, the extent depending on what type of
load.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / manjeet kumar
if u connect 415 secondary side for some hour your load not
operate and transformer secondary side is damage.
Is This Answer Correct ? | 0 Yes | 2 No |
Answer / sanket patil
First of all primary and secondary of a transformer are
decided after putting it in the service. Hence the windings
of transformer are referred as HV and Lv windings.
Now if the HV winding is connected as a secondary then
the xmer will work satisfactorily
In the another case if 220V wdg is connected to the 415V
supply the answer is same as explained by other friends.
Is This Answer Correct ? | 2 Yes | 6 No |
Answer / maan
Most of electrical equipment are rated at 220v,there
working seriously affected if they recive power at haigher
voltage(415v), also losses in primery side increases and
core loss in secondary side , that may damage winding and
insulation.
Is This Answer Correct ? | 1 Yes | 9 No |
In Generator How suction compression power and exhaust works ?
Why we use two wattmeter during block rotor test and no load test of 3phase induction motor? And how can we understand the neat power requirement of from this test?
Why used in layer by layer charcoal and salt used in earth pits.
11 Answers CESC, HP,
Why we use 2core cable for Dc motor.Can I use 3core?
5 Answers JK Paper, Maharaja Whiteline,
what is diffrence between primary & secondry transformer?
Inductor and capacitor ........ power in one phase and ...... it in another phase. if any body found this gaps answer.please sent me to habib_eu2008@yahoo.com
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm
My meter CT is 200/5amps Then my electrical meter MF=???please suggest
what is meant by class 1 E in electrical power supply?
Fault current shall be part of tech specs of power cable or not?.
I have three phase 400 KW,390 A MOTOR.For this motor which type of Cable is required....specifically rubber cable required. Can anyone help me..
how to select DG set for certain load?