In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?
Answers were Sorted based on User's Feedback
Answer / ankaraju
The secondary side is rating of 200v,if you considering
loop the net current flowing throw winding increases hence
losses also increases and winding over heated,if it so on
for hours winding insulation may failed.And another one is
core is nearer to low winding,due to high voltage core
losses and core insulation between laminations also failed.
| Is This Answer Correct ? | 34 Yes | 5 No |
Answer / milan
secondary side winding turns is designed for 200 volts. If
we give 415v the secondary side winding turns will not
sustain the voltage . For which insulation and winding both
will damage .If we give 415v to secondary the primary will
get 816.125v
| Is This Answer Correct ? | 19 Yes | 3 No |
The current at 200v side will be more than what designed
for the transformer and core loss will be more. So
ultimately,transformer will be heated up more faster than
ordinary condition. Depends upon the insulation used for
core construction, and how long u are connected the supply,
there r chances of insulation failiure.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / manoj
as 2ndary side winding is design for 2oo volt so when we
connect 2ndary side to 415 volt,then after some hour the
2ndary winding burnt.
| Is This Answer Correct ? | 9 Yes | 4 No |
Answer / neeraj
the whole transformer will burn up.
i do it practical one time.
but in future i will not do such thing.
| Is This Answer Correct ? | 4 Yes | 1 No |
if Secondary puts 415v, than primary wants to take the
voltage upto 850v, & it can burn the winding of the
transformer.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / partha
In this case, the transformer will undergo insulation
degradation. Also due to the increased voltage, the core
losses will increase. The core will be also subjected to
overfluxing which will cause saturation and increased core
losses.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vino raju dee
200v induced in the primary.there is no application for
this induced voltage.
| Is This Answer Correct ? | 0 Yes | 0 No |
What is the dimension of A4 sheet in mm?
if a 2 ohm resistor,2 ohm capacitor and a 2 ohm inductor is connected parallely to 12v source.Then what is the value of current in each branch.Is current flows in each branch at the same time?If not so then provide the proper sequence
When placed close together, two positively charged materials will
how the B-H loop obtain under the static condition
what is the tolerance for the magnetic balance test conducted on the distribution transformer?
How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer
which type your UPS on line,off line give the reason?
what you mean by frequency of an igbt& how to find it?
how to identify vector group of three phase transformer by voltage method?
What is the si unit
Resistor switching is used in which type Circuit Breaker ? a) oil filled CB b) Air blast CB c) Gas filled CB
11 Answers Engineers India Limited, wbsedcl,
how to reduce the transformer size in ups ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)