Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


In step down transformer (415/200V),mistakenly secondary
side is connected to 415V for some hours, what would be
result of this condition?

Answers were Sorted based on User's Feedback



In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / ankaraju

The secondary side is rating of 200v,if you considering
loop the net current flowing throw winding increases hence
losses also increases and winding over heated,if it so on
for hours winding insulation may failed.And another one is
core is nearer to low winding,due to high voltage core
losses and core insulation between laminations also failed.

Is This Answer Correct ?    34 Yes 5 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / milan

secondary side winding turns is designed for 200 volts. If
we give 415v the secondary side winding turns will not
sustain the voltage . For which insulation and winding both
will damage .If we give 415v to secondary the primary will
get 816.125v

Is This Answer Correct ?    19 Yes 3 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / rvg

The current at 200v side will be more than what designed
for the transformer and core loss will be more. So
ultimately,transformer will be heated up more faster than
ordinary condition. Depends upon the insulation used for
core construction, and how long u are connected the supply,
there r chances of insulation failiure.

Is This Answer Correct ?    11 Yes 1 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / manoj

as 2ndary side winding is design for 2oo volt so when we
connect 2ndary side to 415 volt,then after some hour the
2ndary winding burnt.

Is This Answer Correct ?    9 Yes 4 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / deepakeee

winding will burn

Is This Answer Correct ?    8 Yes 3 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / neeraj

the whole transformer will burn up.
i do it practical one time.
but in future i will not do such thing.

Is This Answer Correct ?    4 Yes 1 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / binay agrawal

if Secondary puts 415v, than primary wants to take the
voltage upto 850v, & it can burn the winding of the
transformer.

Is This Answer Correct ?    3 Yes 1 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / partha

In this case, the transformer will undergo insulation
degradation. Also due to the increased voltage, the core
losses will increase. The core will be also subjected to
overfluxing which will cause saturation and increased core
losses.

Is This Answer Correct ?    1 Yes 0 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / amit choudhary

IT'll as a step up transformer.

Is This Answer Correct ?    0 Yes 0 No

In step down transformer (415/200V),mistakenly secondary side is connected to 415V for some hours,..

Answer / vino raju dee

200v induced in the primary.there is no application for
this induced voltage.

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

What is the dimension of A4 sheet in mm?

6 Answers   Bhel,


if a 2 ohm resistor,2 ohm capacitor and a 2 ohm inductor is connected parallely to 12v source.Then what is the value of current in each branch.Is current flows in each branch at the same time?If not so then provide the proper sequence

1 Answers   Tata Steel Limited,


When placed close together, two positively charged materials will

1 Answers  


how the B-H loop obtain under the static condition

0 Answers  


what is the tolerance for the magnetic balance test conducted on the distribution transformer?

0 Answers  


How much ampere rating on LT side of distribution transformer and also on HT side of 200KVA transformer

2 Answers   ABB,


which type your UPS on line,off line give the reason?

2 Answers   Roto Power,


what you mean by frequency of an igbt& how to find it?

1 Answers  


how to identify vector group of three phase transformer by voltage method?

0 Answers   AAU,


What is the si unit

2 Answers  


Resistor switching is used in which type Circuit Breaker ? a) oil filled CB b) Air blast CB c) Gas filled CB

11 Answers   Engineers India Limited, wbsedcl,


how to reduce the transformer size in ups ?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)