11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
Answer / shailesh taware
1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / manjunath kunigal
one set of tertiary winding CT/PT is sufficient for both
metering and protection.
| Is This Answer Correct ? | 11 Yes | 9 No |
Answer / k n naidu
hi,
one three phase set of PTs for both protection & metering
and one three phase set of CTs with two secondary cores one
for metering and protection are required.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mubanga mulenga
You need:
1)Inst., o/c, Metering & EF - 3 CT's
2) REF - 1 CT
3)SBEF - 1 CT
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vikas chauhan
3 no CT (Double core) for 11 kv side for protection and
metering
3 no CT (Double core) for 0.433 kv side for protection and
metering
11/.110 KV 3 phase PT for 11 KV side
secondry side(.433KV side) phase directly connected for
Metering & select relays for .433 KV secondry voltage.
if you select differencial rotection
3 nos CT for Primary and 3 No CT for Secondry side and
interposing CT for Match and neutralise the current in
relay.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / d ramesh
11KV side(delta)
Line side 3core CT :1No. for metering, O/C&E/F protection,
Differential protection with ICT.
0.433KV(Star)
Nuetral CTs :1core for Standby E/F 5p20
Line CTs :3core CT:1No for metering, O/C&E/F
protection,Differential protection with ICT.
1No. 1-core CT in LV nuetral of Transformer of class 5P20
for earth fault protection.
panel side in the panel itself remaining CTs can be
provided for metering, O/C&E/F, and differential cores with
ICT. In both HV panel & LV panel.
| Is This Answer Correct ? | 2 Yes | 1 No |
what are the safety measures of induction motor?
How do determine the Size of a Droop Current Transfomer for Paralleling of Two Generators, Say I need a Droop Current transformer for a 600 kW generator need to be parallel with a 800 kW generator, etc.
2 Answers JK Cement, MPPGCL Madhya Pradesh Power Generating Company Ltd, PNG Power,
how much importance of power factor in single phase. is it,s importance is quiet same as like three phase power system.
why induction motors are rated at 0.8 power factor.
L.A. (Lightening Arrester) is located at a place from where transmission line enters the transmitting substation. So L.A. (Lightening Arrester) is the first equipments which has to encounter with lightening, high voltage surges and switching surges. It has to absorb energy of lightening, high voltage surges, and switching surges. L.A. (Lightening Arrester) is made up of layers of semiconductors. If these layers can not tolerate energy released by lightening, high voltage surges, and switching surges the L.A. (Lightening Arrester) blasts.
IN A DY11 GROUP DISTRIBUTION TRANSFORMER WITH NEUTRAL EARTHED, WHAT WILL HAPPEN TO THE SYSTEM VOLTAGE & THE EQUIPMENTS IF EARTH GETS OPEN ON LOAD?
What is the purpose of reactor.why we used in over head line?
Explain and give examples about VCB?
0 Answers AZ Engineering, Vodafone,
why DOL starter is use in induction motor as it is not reduce the starting torque
which power plant has high load factor?
define the active power?
what is importance of ka in mccb
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)