11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
Answer / shailesh taware
1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / manjunath kunigal
one set of tertiary winding CT/PT is sufficient for both
metering and protection.
| Is This Answer Correct ? | 11 Yes | 9 No |
Answer / k n naidu
hi,
one three phase set of PTs for both protection & metering
and one three phase set of CTs with two secondary cores one
for metering and protection are required.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mubanga mulenga
You need:
1)Inst., o/c, Metering & EF - 3 CT's
2) REF - 1 CT
3)SBEF - 1 CT
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vikas chauhan
3 no CT (Double core) for 11 kv side for protection and
metering
3 no CT (Double core) for 0.433 kv side for protection and
metering
11/.110 KV 3 phase PT for 11 KV side
secondry side(.433KV side) phase directly connected for
Metering & select relays for .433 KV secondry voltage.
if you select differencial rotection
3 nos CT for Primary and 3 No CT for Secondry side and
interposing CT for Match and neutralise the current in
relay.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / d ramesh
11KV side(delta)
Line side 3core CT :1No. for metering, O/C&E/F protection,
Differential protection with ICT.
0.433KV(Star)
Nuetral CTs :1core for Standby E/F 5p20
Line CTs :3core CT:1No for metering, O/C&E/F
protection,Differential protection with ICT.
1No. 1-core CT in LV nuetral of Transformer of class 5P20
for earth fault protection.
panel side in the panel itself remaining CTs can be
provided for metering, O/C&E/F, and differential cores with
ICT. In both HV panel & LV panel.
| Is This Answer Correct ? | 2 Yes | 1 No |
why we use shunt in a rectifier system ?
what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?
From past few months I am getting lagging pf even though sufficient capacitors used in circuit. Where is the problem pls answer
my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
what is diffrence b/w -48vdc and +48vdc ?
Draw a SLD of HT distribution EB grid up to users Transformer?
A separately excited dc motor having 2 ohm armature resistsance draws a current of 10A and torque developed is 20 Nm under rated field condtion. the speed of the motor under the rated field condtion , when it is connected to a 100V DC source and delivering 10Nm torque....
What are protection of transformer on HT side & on LT side?
what is the instataneous value of voltage in a 3-phase balanced star connected circuit?
What is difference b/w Microwave and OPGW ??
what is apparant power and reactive power
Why we are using LA Rating 10kA in 66 kv substation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)