11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?

Answers were Sorted based on User's Feedback



11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / shailesh taware

1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING

Is This Answer Correct ?    10 Yes 3 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / rakesh

3 ct for metering ,3 ct for protection,3 pt

Is This Answer Correct ?    11 Yes 6 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / priyadharisini

3 nos of CT/PT required

Is This Answer Correct ?    6 Yes 3 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / manjunath kunigal

one set of tertiary winding CT/PT is sufficient for both
metering and protection.

Is This Answer Correct ?    11 Yes 9 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / sandeep

3 CT/1 PT

Is This Answer Correct ?    5 Yes 4 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / senthil kumar

06CT and 03PT'S

Is This Answer Correct ?    3 Yes 2 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / k n naidu

hi,
one three phase set of PTs for both protection & metering
and one three phase set of CTs with two secondary cores one
for metering and protection are required.

Is This Answer Correct ?    1 Yes 0 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / mubanga mulenga

You need:

1)Inst., o/c, Metering & EF - 3 CT's

2) REF - 1 CT

3)SBEF - 1 CT

Is This Answer Correct ?    1 Yes 0 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / vikas chauhan

3 no CT (Double core) for 11 kv side for protection and
metering
3 no CT (Double core) for 0.433 kv side for protection and
metering
11/.110 KV 3 phase PT for 11 KV side
secondry side(.433KV side) phase directly connected for
Metering & select relays for .433 KV secondry voltage.
if you select differencial rotection
3 nos CT for Primary and 3 No CT for Secondry side and
interposing CT for Match and neutralise the current in
relay.

Is This Answer Correct ?    1 Yes 0 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / d ramesh

11KV side(delta)
Line side 3core CT :1No. for metering, O/C&E/F protection,
Differential protection with ICT.

0.433KV(Star)
Nuetral CTs :1core for Standby E/F 5p20
Line CTs :3core CT:1No for metering, O/C&E/F
protection,Differential protection with ICT.

1No. 1-core CT in LV nuetral of Transformer of class 5P20
for earth fault protection.

panel side in the panel itself remaining CTs can be
provided for metering, O/C&E/F, and differential cores with
ICT. In both HV panel & LV panel.

Is This Answer Correct ?    2 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

wat is the advantage of increse in frequency?how the powersupply range decreses as the frequency increses?like in america,it uses 110 ac and 60 hz?

4 Answers  


HOW TO CALCULATE CT AND VT RATIO IN PRTECTION AND METERING?

1 Answers   College School Exams Tests, L&T,


why we used servo motor insted of inducation motor?

1 Answers  


what is the proximity & ferranti effects can you explain to me

1 Answers   APTransco,


What is harmonics. How does it get generated and means to arrest harmonics

8 Answers   Airtel,






Why Delta Star Transformers are used for Lighting Loads.

6 Answers  


what is the kvar, droop, stability,ramp

1 Answers  


Why the rating of the HT breakers are in 1250 Amp, while the load on the breaker is around 50 Amp. ?

9 Answers   Wipro,


difference b/w eath and neutral

10 Answers   ABB,


what is LUX?

4 Answers   NTPC,


Can we manually synchronize two DG sets of same ratings manually without using speed biasing ? If yes then how?

4 Answers  


I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)