11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
Answer / shailesh taware
1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / manjunath kunigal
one set of tertiary winding CT/PT is sufficient for both
metering and protection.
| Is This Answer Correct ? | 11 Yes | 9 No |
Answer / k n naidu
hi,
one three phase set of PTs for both protection & metering
and one three phase set of CTs with two secondary cores one
for metering and protection are required.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mubanga mulenga
You need:
1)Inst., o/c, Metering & EF - 3 CT's
2) REF - 1 CT
3)SBEF - 1 CT
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vikas chauhan
3 no CT (Double core) for 11 kv side for protection and
metering
3 no CT (Double core) for 0.433 kv side for protection and
metering
11/.110 KV 3 phase PT for 11 KV side
secondry side(.433KV side) phase directly connected for
Metering & select relays for .433 KV secondry voltage.
if you select differencial rotection
3 nos CT for Primary and 3 No CT for Secondry side and
interposing CT for Match and neutralise the current in
relay.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / d ramesh
11KV side(delta)
Line side 3core CT :1No. for metering, O/C&E/F protection,
Differential protection with ICT.
0.433KV(Star)
Nuetral CTs :1core for Standby E/F 5p20
Line CTs :3core CT:1No for metering, O/C&E/F
protection,Differential protection with ICT.
1No. 1-core CT in LV nuetral of Transformer of class 5P20
for earth fault protection.
panel side in the panel itself remaining CTs can be
provided for metering, O/C&E/F, and differential cores with
ICT. In both HV panel & LV panel.
| Is This Answer Correct ? | 2 Yes | 1 No |
what is the difference between servo voltage stabilizer and general voltage stabilizer?
Going in for a three phase motor or a single phase motor, what factor should be considered for this? For eg., to pump water to certain height and such domestic applications, which motor is suitable?
Is there is any hazard to insulation of 3hp motor 5 KV megger is used for it?
can u please tell me how VFD(variable frequency) drive is used as a energy saver....?
what does mean of RCT and STR in diffrential CT?
IN 500 KVA TRANSFORMER 11KV/415 VOLTS HOW TO CALCULATE THE HT CABLE SIZE AND LT CABLE SIZE FROM TRANSFORMER TO LT PANNEL. AND HOW MANY MAINSWITCHES OR MCBS WITH RATING ARE TO BE PROVIDED
What will be the current rating of Main switch for 80 kVAR panel
when is the Ohms law is applicable?
why we use copper earthing for neutral while for body GI.
1 Answers Chennai Metro Rail Limited CMRL, Valeo Lighting Systems India Private Limited,
can any one help me out by posting something related to rvnl interview for site engineer electrical.? what is the procedure? what kinda question they ask us? how long the interview goes? and any tips? and any thing you want to share?
Dear all: Recently we got a question about Interface between PMS and SAP-PM.once we got a update message from PMS.we should set the deletional flag for functional location in SAP system.Is there any FM or BAPI to use?There are only functional location create and change provided by SAP. Best regards!
What kind of socket shall be provided for window type air conditioner with cooling capacity upto 18000 BTU/hr
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)