Answer / satish babu
Consider two parameters to descide the CT ratings,
a) Primary current on the phase is 1050 amps,Consider No of
leads it has from the generator - If one cable is connected
your primary can be 1000A-1200A
If two leads are used , use only one lead as CT primary
then the CT primary can be 500-600 A
b) Your secondary can be 3A / 1A / 0.5A depending upon the
AVR used
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / r.nombri
Haven't really used a Droop CT. Droop is the decaying of
current from it's initial peak/input, so your trying to
maintain synchronism of two generators in parallel with a
droop CT. By which the Droop CT may be used to improve the
secondary output connection between the two generators with
respect to their rated VA, and kW.
R.Nombri
| Is This Answer Correct ? | 0 Yes | 5 No |
what is volt drop formula?stm
What will be the change in its efficiency and other parameters of a ONAN transformer if it changed to ONAF transformer ?
how to calculate the battery AH
generally on the roadside v hav 11kv line which is being step down to 440v line to line....so any1 can tell me which type of transformer they r using whether it is star to delta,delta to star etc...???
For an induction motor wat is the loading/unloading cycle duration or interms of L/UL ratio/ percentage?
explain Density
please explain working of revers power relay
what is difference between ac1 and ac3 contactor and why it is needed to be selected?
Hi.. I am a BE GRaduate in E&E. I have 8.5 Experience in Tendering & Estimation field. I have done SAP SD course few years back. But due to some reason i failed to get job in that field and continued my own field. Now I am thinking of changing into SAP seriously. How should i go ahead???
what is amf panel & how it is working
Can anybody tell me why inductors draw lagging current and capacitors draw leading current from supply?
why near the transformers, the Jelly(small white colored rocks)are poured.and what are conditions for that?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)