How do determine the Size of a Droop Current Transfomer for
Paralleling of Two Generators, Say I need a Droop Current
transformer for a 600 kW generator need to be parallel with
a 800 kW generator, etc.
Answers were Sorted based on User's Feedback
Answer / satish babu
Consider two parameters to descide the CT ratings,
a) Primary current on the phase is 1050 amps,Consider No of
leads it has from the generator - If one cable is connected
your primary can be 1000A-1200A
If two leads are used , use only one lead as CT primary
then the CT primary can be 500-600 A
b) Your secondary can be 3A / 1A / 0.5A depending upon the
AVR used
| Is This Answer Correct ? | 8 Yes | 3 No |
Answer / r.nombri
Haven't really used a Droop CT. Droop is the decaying of
current from it's initial peak/input, so your trying to
maintain synchronism of two generators in parallel with a
droop CT. By which the Droop CT may be used to improve the
secondary output connection between the two generators with
respect to their rated VA, and kW.
R.Nombri
| Is This Answer Correct ? | 0 Yes | 5 No |
what do u understand from filter factor of reactor?
11 kg trivevter meter has rating of -/5amps. And pt ratio11000/110v and is connected with 11kv ct/pt unit of cr ratio 75/5amps. And pt ratio of 11000/110v while checking accuracy of meter with HT Accuchek meter what value of PT ratio and CT ratio to be filled in Accuchek meter
Cables Construction hi friends, 0.6/1/1.2 kV LV , DC and Control cables are concentric copper conductor what does its means and what is the use of concentric copper conductor,and are this with copper tape shield or copper screening, ? thanks
what is the chemical name for oil that used in the transformer
How to identify phases in the transformer like motor and AC generator but one condition without phase indication like(RYB,UVW)?
Hi, We have have the major losses between BBT ( Bus Bar Trunking) to LT Incomer & LT to HT incomer, how to arrive the losses?
n1 =1000 n2 =?;v1 =200:v2 =400
typically in power distribution substation. 1- Any idea how would be the graph of capacitor bank consumption verses time through the day . 2- How is the switching ( on and off ) of the capacitor bank, per need?
how to electronic energy metter failed in electomagnectic fild passing in the metter and which thing to defect more on metter.
are there rmu for 3 transformer?
How to check the efficiency of the generator , air compressors.
how to select the automotive wire size by mathematical calculation. for xenon headlamp with ballast. the ballast given data voltage 10-17v,current permenant 6amp, run up phase is 15amp, peak at swicth on max 400micro sec is 40amp.the sum of cable resistance is 150mohm.please provide referenc document if any for relating the peak at switch on current,time & wire wire size
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)