11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answer Posted / shailesh taware
1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING
| Is This Answer Correct ? | 10 Yes | 3 No |
Post New Answer View All Answers
how to calculate the formula of cable size if motor kw is given
how tto ingress mw in turbine explain.procedure ?
How we calculate DC inducation moter Amp? Sir pls give me formula......
diff b/w normal grounding and resistance grounding
What should be current in the Primary and secondary side of 1000KVA (11KV Supply)Transformer.?
Why does the Solid state Rectifiers for 3-ph brake motors sometimes have 2 & sometimes 3 output terminals?
how to identify vector group of three phase transformer by voltage method?
what is destructive and non-destructive testing of welding
How can we calculate the efficiency of a Running (On-Load) Motor ? What parameters are required and what is the method ?
what is transformor oil gread
compare between starting charactristics of synchronous motor with those of 3Q Squirrel cage induction motor
what is the reactive power what is the use of it in system
what is the difference between directional & non directional earth fault with example please explain.
What is the diffrence (Technical & Construction ) between CBCT & Normal CT?
what is rating boiler