Answer / dinesh. r
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm.
| Is This Answer Correct ? | 478 Yes | 30 No |
Answer / shanmu
Earth Resistance is measured by the device'EARTH MAGGER'.
| Is This Answer Correct ? | 300 Yes | 121 No |
Earth resistance can be measured using Megger instrument.
| Is This Answer Correct ? | 335 Yes | 180 No |
Answer / r.sarkar
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm.
| Is This Answer Correct ? | 116 Yes | 19 No |
Answer / dinesh kumar
1.To measure earth resistance we use Earth Resistance
Meter/Megger.
2.In this Megger there are three terminals
Line,Nuetral&Earth.
3.Line & Nuetral are connected to two terminals and EARTH
Terminal to earth pit to be measured for resistance.
| Is This Answer Correct ? | 169 Yes | 77 No |
Answer / ullas
using two methods:
1.fall of potential method
2.earth tester(device)
factors affecting earth resistance are
1. Shape & material of the earth electrode.
2. Depth of the electrode at which they r burried in soil.
3. Specific resistance of the soil surrounding the electrode
(Specific resistance of the soil varies depending on
moisture content in the soil..... varies from 80*10^3ohm-m
to 80*10^6ohm-m)
| Is This Answer Correct ? | 74 Yes | 19 No |
Answer / k.viswanathan
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
| Is This Answer Correct ? | 55 Yes | 12 No |
Earth resistance measured by using earth tester.
| Is This Answer Correct ? | 40 Yes | 12 No |
Answer / natarajan
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
| Is This Answer Correct ? | 24 Yes | 15 No |
all electricals questions
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
why are use star delta startor.
we have provided 30 mA rccb to water cooler.but we feel shock in cooler body.what is the reason?
CAN U PLEASE TELL ME SOME G.D TOPICS FOR APGENCO INTERVIEW&G.D
shall we use a machine having 60Hz frequency in india ? why?
What is the difference between AC Drive and VFD?
Logic using 1 kV or 1,1 kV grade in house wiring Low voltage cable. Explain/suggest? some use 1kV and some prefer 1.1kV grade insulation low voltage cable why??
What do you mean by an instrument transformer?
WHAT IS FORMULA TO KNOW TO BACKUP TIME OF POWER PLANT 48V/50AMP DELTA POWER PLANT
In Indian Railways , how the AC motor is driven? Please explain clearly starting from the overhead 25kV supply.
How to calculate the fuel consumption for 600kva DG genset which connecting with 25%load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)