Do you know how to measure the earth resistance? if so
explain it
Answer Posted / dinesh kumar
1.To measure earth resistance we use Earth Resistance
Meter/Megger.
2.In this Megger there are three terminals
Line,Nuetral&Earth.
3.Line & Nuetral are connected to two terminals and EARTH
Terminal to earth pit to be measured for resistance.
Is This Answer Correct ? | 169 Yes | 77 No |
Post New Answer View All Answers
How many sprinklers should be in one pipe line?
what is the meaning of 5% droop or 7% droop in AVR?
Hi Everyone ! My Name is Hakim ullah khan please i need formula of Cable Rating because i want to calculate by self without check any Table Chart... Thank you.....
i will applied in 1U-1W on 440 volt primary delta side. what is the result of magtic balance test
How to derive detailed design of Suitable bus Bar for 100A for 6.6KV?
What is the difference between hot and cold loop testing?
Why use the vcb at high transmission system ? Why can’t use acb?
what is magnetizing current test in power transformer
With a phasor diagram show the effect of increasing the field current of a generator supplying a constant real power and connected to a grid system.
How to calculate earth wire load by formula
How shall i select the value of capacitor or inductor in a system?
5.WHICH TYPE WELDING PROCESSES USES NON CONSUMABLE ELECTRODE.........
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
What are the causes of unbalanced current on 34.5kv feeder Ia=0.05,Ib= 0.25, Ic=0.15 and In=0.27 prior to tripping current are balance?
Which type of transformer is used for lighting loads?