Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is ups?how its works?and what is there in static
switch how it works?

Answers were Sorted based on User's Feedback



what is ups?how its works?and what is there in static switch how it works?..

Answer / thowsif_emerson_csm team

Working Principle of UPS:-
UPS is for the purpose to give un-
interruptible power
supply. This stores the energy in the form of DC by the
controlled rectifier (AC - DC converter) and discharge the
energy in the form of controlled AC by inverter (DC - AC
converter) so as to provide continuous power supply. Here
the back up is derived based on the requirement.

types:
1. Online Double convertion UPS (Normal High capacity UPS)
2. Online Delta convertion UPS (New technology offline
using buck boost Transformers)
3. Offline UPS (economical UPS medium capacity UPS 3 -
30KVA also available in higher capacity)
4. Line Interactive UPS (lower capacity UPS 300VA - max5KVA
output will be Squasi Sinewave).

UPS are used in home, medical, IT and industrial where the
critical load is used.


Static Transfer Switches :-

Static transfer switches in single
phase and 3 phase outputs suitable for use with two
synchronised or non synchronised input power sources, the
transfer switch provides a single output to the critical
load. This series of static transfer switches can operate
with the default source selected as A or B to feed the
critical load, on failure of the selected source the load
will be transferred in synchronism to the alternative
source. Sizes are available from 10kW to 1000kW with three
switching elements as standard for the three phase system,
a manual wrap around bypass switch is also provided. A
power flow status mimic and alarm indicating mimic with
separate digital or analogue metering is fitted as a
standard feature.



Is This Answer Correct ?    16 Yes 3 No

what is ups?how its works?and what is there in static switch how it works?..

Answer / sakkaravarthi soganur

ups means un interuptible powersupply

ac voltage converted to dc voltage through converter
dc supply connected to baterry also connected to inverter
incoming so we convert dc to ac through inverter.whenever
normal supply failure at that time battry suplly used
without any interuption,
static switch means two scr's connected to antiparallel,and
also this is electronics switch,

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

Whether amorphous core transformer is available in India?.If available then up to what rating of voltage and KVA?.

0 Answers   DAE, Tata Chemicals,


The importance of resonant filters in converters?

1 Answers  


What are the different modes of plc processor?

1 Answers  


This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????

2 Answers  


why shoud in High tension cable( above11KV etc.,)a semiconducting material coating will be there on insulation?

1 Answers  


what ever the ups kva it may 500 kva or 500 va always out put is AC 240 volts its right?

3 Answers  


a distribution transformer(3 phase)supplying 440volt per phase.now suppose one of phase voltage(230volt) becomes zero.what will be the cause ?

3 Answers  


Can we connect two CT'S to one energymeter?

1 Answers   KSEB,


why generation is done in delta nad transmission in star? brief

3 Answers  


HARMONICS ARE ALWAYS IN INTEGER LIKE 2ND OR 3RD HARMONICS,NOT IN FRACTION LIKE 0.5 HARMONICS.....????????

2 Answers  


what is the different between bus section and bus coupler

1 Answers  


is there any concept of armature reaction in Induction motor?

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)