Do you know how to measure the earth resistance? if so
explain it
Answer Posted / natarajan
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
| Is This Answer Correct ? | 24 Yes | 15 No |
Post New Answer View All Answers
what is basic difference betmeen normal & flame proof motor??
What is the IS standard for MCCB to be use (As per capacity of AMP)& for ACB also.
What is mean 2XWY
which type of questions asking for solar companies?
Why you are switching off arc protection mcb when you are taking shutdown for lv board.
What is the function of electron gun assembly used in crt?
What is the working mechanism of OLTC in Power Transformers????
how to calculate earth fault relay current and CBCT ratio
What will happen if the d.c. Machine is operated below rated speed?
Approach of a cooling tower is the difference between temperatures of what factors?
what is RNG in the DG synchronizing by PLC?
What is nichols chart?
How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.
How are load losses and no-load losses measured at site in a DG set?
what is the differance between HT motors And LT MOTORS.