What is GIS (Gas Insulated Switchgear)

Answers were Sorted based on User's Feedback



What is GIS (Gas Insulated Switchgear)..

Answer / virendra

GIS means Gas insulated Substation.

In this all the Switchgear like Circuit breaker, CT PT,
Isolator all kept in one champer filled with SF6 gas 1t 4
kg pressure
It aquires less space

Is This Answer Correct ?    6 Yes 1 No

What is GIS (Gas Insulated Switchgear)..

Answer / hanupowergrid

It is very much required to establish an electrical substation at load center. Since, establishing a substation at load center is quite economical and profitable in many aspects. As it reduces length of feeders and due to short length feeders, the quality of voltage regulation improves. But the main obstruction of establishing a substation at load center is space. Generally main load center of any place is situated at very congested place where, sufficient land for establishing conventional electrical substation is very hardly available.

his problem can be solved by using gas insulated switchgear technology. In this type of switchgear, all the necessary components of switchgear can be assembled in very limited space. GIS is a kind of metal enclosed switchgear. That means, all the equipments of the electrical switchgear are enclosed by gas tight metal enclosure and SF6 gas is used as insulation between live parts of the equipments and earthed metal enclosure. This type of switchgear, means, gas insulated switchgear is available from 12 KV system to 800 KV system. For establishing electrical substation in very limited place this type of SF6 insulated electrical switchgear plays the major role.

Gas insulated components of substation are generally,

Electrical bus bars.

Electrical isolators or disconnectors.

Circuit breakers.

Current transformers.

Voltage transformers.

Earth switches.

Surge arrestors or lightning arresters.

The substation, assembled by gas insulated switchgear, is popularly known as gas insulated metal enclosed substation (GIMES). GIMES technology is not very recent invention, it is successfully running for over thirty years. In gas insulated medium voltage switchgear, vacuum technology is used as interrupting purpose and SF6 gas is used as insulation material. Although for both interruption and insulation, SF6 gas is used in many medium voltage GIS system. But for such equipments rated SF6 gas pressures are different for interruption and insulation. SF6 gas pressure for insulating purpose is generally kept below 2.5 bar whereas SF6 gas pressure for interrupting purpose is ranged from 5 bar to 7 bar. As vacuum technology is not available for high voltage, so for GIS or gas insulated switchgear system above 72.5 KV, only SF6 is used both for interruption medium and insulation. There are different types of gas insulated metal enclosed switchgears available depending upon their constructional feature.

Is This Answer Correct ?    2 Yes 0 No

What is GIS (Gas Insulated Switchgear)..

Answer / m.vijayaragavan

HI,

THE EAQUIPMENTS IN THE SUBSTATION ARE INSULATED EACH
OTHER WITH GAS. NORMALLY THE INDOOR SUBSTATION WE SAYING AS
GIS. .IN OUTDOOR SUBSTATION THE EQUIPMENTS ARE INSULATED
WITH AIR.

THANKS,
M.VIJAYARAGAVAN,
TECHNO ELECT LTD,
KOLKATA.

Is This Answer Correct ?    3 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Is it advantages of having star-delta vfd than normal star vfd , if yes why?

0 Answers  


in three pin plug 6 Amp. 220v AC rating. why earth pin diameter is higher than ohter two pin? what its purpose ?

6 Answers  


What is converter transformer? Diff b/w converter transformer and distribution transformer? why we use converter transformer in place of giving supply to drives?

1 Answers  


Explain working of servo controlled voltage stabilizer.

3 Answers  


What is the difference between grid and off- grid system??

0 Answers   GVK,






Send the control circuit digram of a star delta stater?

1 Answers   L&T,


how to test the electrical panel.ht lt mcc pcc.

0 Answers   Ambience, Shivalik,


What is genrally the % Impedance of a Dg set? How can we calculate Earthing conductor size for a DG set?

0 Answers  


how the transmission voltage ranges are decided like 11kV,33kV,66kV,132kV,220kV,400kV,725kV.... why not choose the transmission line voltage as 23kV,164kV,440kV?? what's the reason??

3 Answers  


What makes the difference between 50Hz supply and 60Hz supply which one is economical and how can you support your answer...........?

2 Answers   Fertichem, Kuwait Oil Company,


what is mean by Digital Logic Meter (DLM)

0 Answers  


Is there any scope for an electrical engineer in MRF company......

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)