why restricted earth fault protection can not operate for
phase faults??as there will be a current in secondary of
ct,when a phase fault occurs!
Answer / tapas
* In REF scheme 4 nos of CTs are used. 3 for phase and 1 for Neutral.
* It operates in the principle of balance current between phase and neutral and only inside In-zones. i.e. it protects Transformer, Busduct, LV switchgear.
* In this protection phase CTs are connected in such a way that it forms a close path between phase CT secondaries and this close path is connected with neutral CT secondary.
* In between the close path connected to common terminals of phase CT secondary and Neutral CT secondary REF relay is connected.
* When a phase fault occurs there is also residual current in Neutral. So current between both paths oppose each other and hence there will be no current in REF relay. So it won't operate.
| Is This Answer Correct ? | 1 Yes | 0 No |
Why generator is not connecting in delta ..why connecting in star ?
4 Answers Bhel, Foretec Engineers,
what is skin effect?
what is form factor?
1 sq mm conductor=? how many amps
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
What is Ton Capacity of Air Conditioner?
Why we use Delta connection in the secondary side of a High Voltage transformer?
Why the dc voltage drop during starting of emergency lube oil pump? The Voltage drop from 135kv to 125 kv for one min. before re-establish to 135kv?
WHAT IS IM (INDEX OF MOUNTING )IN MOTORS
What is complex power?
Please tell me if you are electrical engineer,and you are appointed for the maintainance of Electrical Power plant,then which parts of the plant deal with you.Also tell how these parts/components work.
what is the formula of starting current of 3phase and 1 phase motor???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)