why restricted earth fault protection can not operate for
phase faults??as there will be a current in secondary of
ct,when a phase fault occurs!
Answer / tapas
* In REF scheme 4 nos of CTs are used. 3 for phase and 1 for Neutral.
* It operates in the principle of balance current between phase and neutral and only inside In-zones. i.e. it protects Transformer, Busduct, LV switchgear.
* In this protection phase CTs are connected in such a way that it forms a close path between phase CT secondaries and this close path is connected with neutral CT secondary.
* In between the close path connected to common terminals of phase CT secondary and Neutral CT secondary REF relay is connected.
* When a phase fault occurs there is also residual current in Neutral. So current between both paths oppose each other and hence there will be no current in REF relay. So it won't operate.
| Is This Answer Correct ? | 1 Yes | 0 No |
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
what is the difference between power and distribution transformer?
32 Answers L&T, VJTI, Wenke Electricals,
How do I know if a transformer is saturated? I am doing the simulation of the saturation of a transformer, but what parameter tells me when a transformer is saturated? How do you calculate? is on the plate?, there is a rule that can help me? How could model? I understand the saturation occurs when the flow can no longer bind to the other winding, this is given to certain current, this current is the same that appears as the highest in the bale of features? Thank you for your help Eduardo Alvarez Guatemala
In UPS what does 600va reffer to?
why the rotor current becomes in steady state during high slip region? please verify with equations.
please send me previose rrb junior engineer qustion papers
3 phase supply is there Total kw 100 howmuch cable put the load
is synchrnous pannel is need for two eqal rating transformers to run in parallel
Why smallest capacity LV motor are star connected and medium & bigger size LV motors are delts connected
What is the result of under frequency to the system.
what is second harmonic, how is effect transformer ?.
Why we use a shunt capacitor or synchronizing Motor To Improve a Power factor pls reply me in this mail dinesh_elect_eng@yahoo.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)