Answer / sharma jiten
The most common method for improving power factor is to add
capacitors banks to the system. Capacitors are attractive
because they're economical and easy to maintain. Not only
that, they have no moving parts, unlike some other devices
used for the same purpose.
When you add a capacitor bank to your system, the capacitor
supplies the reactive power needed by the load. If you size
and select the capacitor bank to compensate to a unity
power factor, it can supply all the reactive power needed
by the load, and no reactive power is demanded from the
utility. If you design the capacitor bank to improve the
power factor to a quantity less than 1.0, the reactive
power supplied by the bank will be its rated kVARs (or
MVARs), while the rest of the reactive power needed by the
load will be supplied by the utility.
| Is This Answer Correct ? | 139 Yes | 11 No |
Answer / vara prasad
guys this question does't mean that to specify your
company's capacitor bank capacity .... please answer in
general how to calculate your required capacity of
capacitors at your company depending on load
| Is This Answer Correct ? | 36 Yes | 3 No |
Answer / chandru
The addition of capacitance depend upon your power factor.suppose u may get more than 0.97 or unity Pf,u no need to add capacitor.becoz it may act like load
| Is This Answer Correct ? | 9 Yes | 1 No |
Power factor is only present in the ac power supply systems. In dc there is no usage of power factor terms. Ac supply is having frequency and potential is alternating with respective to time as such the load on the ac power source is of mix like capacitance, resistance and inductance
Capacitance is offered by ug cables and heater and filament lamps offer the resistive loads and hid and fluorescent lamps offers inductance value
Inductive reactance (xl) and capacitive reactance (xc) is counter each other and resultant effect will reflect in ac system in addition to normal resistance. This cumulative resistive effect is called as impedence.
Now power factor is equel to pf = r/z.
Now if we draw a power circle the you know the differnce of kw and kva is made by kvar that is reactive power if we reduce this reactive power then the kva demand and kw i mean apparent power and actual power will became more or less equal. Now power factor that is quality power.
So we can improve the power systems by adding counter reactive power by adding capacitors in kvar ratings.
Apfc panels are best suitable for proper monitoring as static correction will not perform well in massive load centres as failure and degradation of capacitor is hard to find out and rectify.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / natrayan
I Need to know the how much capacitor bank that i have to put for these Load KW or HP or KVA
For Example: 15HP we can use 2kVAR of capacitor
like that?...
| Is This Answer Correct ? | 9 Yes | 5 No |
The correct method for PFC is to calculate how much correct you need.
If you know the PF and Pd of a motor being used on average, and want to improve to 90%p.f. then compute then angle of PF before and after from theta=cos^-1(PF) then take difference in tan (theta) * Pd
Good to Know:
Important formulas which is used for Power factor improvement calculation as well as used in the above calculation
Power in Watts
kW = kVA x Cosθ
kW = HP x 0.746 or (HP x 0.746) / Efficiency … (HP = Motor Power)
kW = √ ( kVA2– kVAR2)
kW = P = VI Cosθ … (Single Phase)
kW = P =√3x V x I Cosθ … (Three Phase)
Apparent Power in VA
kVA= √(kW2+ kVAR2)
kVA = kW/ Cosθ
Reactive Power in VA
kVAR= √(kVA2– kW2)
kVAR = C x (2 π f V2)
Power factor (from 0.1 to 1)
Power Factor = Cosθ = P / V I … (Single Phase)
Power Factor = Cosθ = P / (√3x V x I) … (Three Phase)
Power Factor = Cosθ = kW / kVA … (Both Single Phase & Three Phase)
Power Factor = Cosθ = R/Z … (Resistance / Impedance)
XC = 1/ (2 π f C) … (XC = Capacitive reactance)
IC = V/ XC … (I = V / R)
Required Capacity of Capacitor in Farads/Microfarads
C = kVAR / (2 π f V2) in microfarad
Required Capacity of Capacitor in kVAR
kVAR = C x (2 π f V2)
| Is This Answer Correct ? | 6 Yes | 3 No |
Minimum IR value of 1.1 kv grade 3.5c (300, 240,185,150,120,95,70,50,35,25) sqmm Aluminium XLPE cable and 4c (16, 10,6 & 4) sqmm cu arm cable between RY,YB,BR,RN,YN,BN,RE,YE,BE & NE.
how cables go in and come out for distribution from the feeder pillar box?
what will happen if the input of a transformer is dc?
how voltage regulator works ?
what's the difference between abs/inc encoders. apart from the position remembrance what are all the other differences. and what's mean by grey code.
how to calculate the transformer losses.
in our all power plant have connected in grid and grid voltage and plant voltage is same, but as per as electrical concept the power will transmit from high potential to low potential but here altough same,then how power transmit from power plant to grid.
Why efficiency of generator is higher than motor at a particular load?
i have installed my solar site of 6.7kw and is working perfectly , can somebody tell me that how can i measure my solar irradiation kw/day/sq m ?
what is differance bw ELCB and MCB. ?
Why single phase induction motors are not self starting ?
what should be the megger test report for 11KV cable when meggered with 5KV megger , what is the resistance value we should get
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)