we have two 11/.433 kv. distribution Transformer rating as
1000 kva & 500 kva , i wants to run parallel both transformer.
both transformer impendence voltage is 5.24%, How can we run
both t/f, & how sharing the load
Answers were Sorted based on User's Feedback
Answer / kandasamy
Since both the trasformers are identical impedance , The
load sharing will be exactl equal OF TOTAL (LOAD)POWER.
Load sharing of transformer A= Power x(ZB/ZA+ZB).
Load sharing of transformer B= Power x(ZA/ZA+ZB).
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / aks
Both the trasformers will share the load equally.ie.50% by
each transformer.
Is This Answer Correct ? | 1 Yes | 0 No |
As mentioned if the capacity, the vectror group ,
Impedance is equall you can connect both the transformet
in parrel just make sure that the Phase sequence for both
the transformer is same at the time of parallel & as the %
impedance is same the laad sharing will be equall.
Is This Answer Correct ? | 0 Yes | 1 No |
What is the effect of impedance on the heat losses in case of AC system??? Does heat losses really depends on the impedance or depends only on resistive component only..??
What will be the output of an alternator ,if the field current is single phase ac supply.
how i chosse capacitor bank if my energy meter is 48 kvr? tell me capacitor bank chossen formula?
usually why bettery voltage are 1.5V, even if you open a 9V battery there are six 1.5V batteries in series. is it not possible to increase this voltage other than putting in series
what is dc voltage?
what are the types of starter ?
25 Answers Andhra Sugars, Bhel, Eveready, HyFun Foods, Jindal, ME, Valeo Lighting Systems India Private Limited,
explain in detail HV & LV bushing connection in power transformer (110 / 11 kv 16 MVA)
6 Answers TNEB Tamil Nadu Electricity Board, wbsedcl,
what will hapen if we give ac supply to dc motor?
What is the GI Earth Flat Size recomended for 33KV 2000KVA Distribution Transformer
What are root loci?
how to find out cable size if load is 2800 watts, 230 volts AC supply and load distance is 1800 meters
Why donot sleep below the tree for night time?