What is the rating of your capacitor bank at your company.
Answers were Sorted based on User's Feedback
Answer / sisir kumar singh
the general principle of installing capacitor bank is
take 35% of the connected load.and in a capacitor bank put 12 -15% as a fixed capacitor.
suppose your connected load is 1000 kw then the capacitor bank size will be 350 kvar and the fixed capacitor will be12-15% of 350 kvar that is 42 -53 kvar
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amanpreet singh
240V to 2490V and size of 2.5kvar to 1000kvar
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / manjunath.m
Maximum we can connect the capacitor bank 40% of the
contract demend.
EX: our Bescom contract demand is 1000 kvar.
we can connect up to 400kvar capacitor bank panel.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / md.nur nabi hossain
for 11kv , capacitor bank will be1500kvar.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / suresh kumar
The capacitor maintained current load and the power ffactor 0.91 to 0.99 is correct values of capacitors in ac supply and DG set of pf is 0.85
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shubhanshu
in my company we have installed two capacitor banks of 3.242 MVAR to improve the power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
how to calculate cable size, olr rating, contactor rating and mccb rating,to below given details three phase motor 75 kw,415 v,.85 pf,50 hz?
what are the functions of fuse ?
What’s electric traction?
how to reverse the direction of universal motor?
explain the application of reciprocity theorom
how to calculate short circuit breaking capacity KA for 2500kva 33kv transformer.
We have energy meter of ct ratio 200/5amp and installed cut having ct ratio 100/5 amp what is final MF?
in my industry we are using 3 step up transformers for induction heaters..i.e 415/580v and other are 11/440v.in power consumption does a step trnsformer makes any difference compared to step up?? plz explain
What will be the size of cable required for 5.5 KW motor ( Full load current 10 Amps approx.), Starting current with DOL is 120 Amps. Aprrox. Short circuit current with LLLG fault is 2000 Amps Approx.
We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?
for high freq ac,why we first convert AC to DC and then DC to high freq.AC
what is buffer resistance starter.?.What is the working principle and where it is used..?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)