what sud u do if u dont get feedback from control valve?
Answer / carl_ellis
There's two kinds of feedback from a control valve:
a) the change of the process variable because the valve
position changes
b) position feedback directly from the positioner to the
controller/control system.
We'll assume that the question is directed at the loss of
position feedback signal from the loop's positioner.
1) Position feedback cards are options on smart
transmitters and need to be initialized after installation.
Has it been initialized?
2) DC power is typically loop power for position feedback.
Is the loop power supply still functioning?
3) Has the position feedback card or its wiring been
disabled or removed?
4) If the position feedback loop is intrinsically safe, is
the loop's I/S barrier open circuited?
5) Has the loop wiring been changed in some manner so as to
affect the position feedback signal integrity?
Carl Ellis
Measure First
| Is This Answer Correct ? | 8 Yes | 0 No |
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
What is the Temperature Co-officient of Resistance of PT- 1000 and PT-2000 ?
how to convert bar to mA?
HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS
If mVolts can drop by resistance of wire as compare to mA, then how thermocouple mV reaches in CCR as accurate value?
What is i/e or o/p transmitter(ma/v)?
Yokogawa mass flow meter shows negative reading...what r the main causes for this problem?...
Define all the process Variable and state their unit of measurement. ?
How to set up the various advanced process controllers, input the proper parameters, and tune those controllers given related control system information.
Where Can i take a SPI INtools training in Mumbai? In Rolta India Ltd to whom I should approach regarding of SPI INtools Training?
Which boiler is use in power plant
How can we say that accuracy of measurement increases by using 3 or 4 wire RTD? because for example: If resistance of RTD element is say r ohms and Resistance of the cable from transmitter to RTD is R ohms And if 4 wire RTD is used, ____._____________________ R ohms | |_____._____________________ R ohms / \ / r ohms \ \ | |______.__________________ R Ohms | |_______._________________ R ohms Then the actual resistance measured will be: Total = r + R/2 + R/2 = r +R Ohms Note: r+R instead of r ohms. hence error
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)