how to calibrate displacer type level transmitter by dry
weight method please mention formula for weight calculation
Answer / vikash suthar
here you have not mentioned that displacer is used for single
liquid measurement or Interface level my answer is for single
liquid measurement.
For zero take the weight equal to the weight of the float or
simply hang the float then give the zero
For span take the sp.gravity of the liquid and then take the
volume of the float by pie x r2 x h (r2 is the radius
square)and h is the height of the float.
multiply this sp.gravity and the volume of the float.that
will be the weight of the liquid displace by the float.
Then subtract this weight from the weight of the float that
much weight hang on by replacing the float and give span.
Is This Answer Correct ? | 14 Yes | 3 No |
Why the tapping connections are taking above for gas service and below for liquid service?
You wish to SINK all my digital inputs to a PLC digital input card. Would you common out the leads to a positive or a negative connection?
So I'm a first year apprentice and I'm having a tough time with knowing the difference between AI, AO, DI, DO. I'm having a hard time understanding what devices are which and why. Can someone explain this to me?
how to calculate orifice sizing? and tell me if pipe size bet 50mm t0 200mm then we can use pipe flange??? and above 250mm pipe size should i use D & D/2 Flange? is it right or wrong?
What is mean by Adapter block and net block?
how to convert bar to mA?
WHAT IS TMXT IN TEMPERATURE FOUNDATION FIELDBUS.
If hart communicator provide 4-20ma source to any transmitter during the callibration?
how we will install a positioner ?
In which principle Woodward Governor 505 work in power plant? What are the input of Woodward governor 505
Dear Sir/Madam, I am attending an interview for ETs in BHEL. I have cleared my written test under Electronics (Instrumentation). This is the first time I am appearing for an interview. Can any one who has attended the interview earlier give me a clue to face the interview. With regards Sindhu
What is the processor scan time of allen bradle control logix processor 5555 lenin lenin123us@rediff.com