Answer / carl_ellis
Calibrating a point level switch
Contact level switches detect the presence or absence of
the medium, whether solid or liquid, by direct contact with
the medium. The switch output for most devices is an
on/off binary signal that reflects the presence or absence
of the medium. Some level switches use a 4-20mA output
that does not modulate, the current signal is either 4mA or
20mA, depending its detection state.
Most level switches offer some form of sensitivity
adjustment (depends on the technology) and some have an on-
delay or off-delay adjustment of the output relay trip,
used to avoid nuisance trips.
Calibration consists of
- testing whether the switch output changes state when the
presence or absence of the medium is changed and adjusting
the sensitivity setting for the specific medium used with
the switch.
- whether the on-delay and off-delay settings comply with
the requirements of the installed application
Depending on the technology, there might be sensitivity
adjustments or on-delay or off-delay adjustments, which are
specific to the installed application, and a calibration
would cover.
A non-contact level switch, like Siemen ultrasonic ULS200,
can be tested in place by comparing the reading with a
physical distance measurement (tape measurement) or out-of-
process by shooting against a solid target and measuring
the distance to check the trip and reset setpoints.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
please explain smoke detectore & lel detector?what is o/p
pls give me presant awerness quistion and answer in my emailid.
what is the function of boiler in plant?
Explain the difference between mmwc and mmwg?
What is cascade control in process instrumentation?
4 Answers Engineers India, ITC Infotech,
While preparing the graphic diagrams trend display, 3 types of trends are prepared by Yokogawa system vender. These are for process variable, manipulated variable & set point variable. Why these 3 trends are required? Explain the purpose of these 3 trends.
How to connect PLC to DCS ?
how to calculate MMWC values in to Tonns(MMWC values showing in DP transmitter and Tonns value showing in Totalizer). please tell me details?
What denotes the 5/8mm in the 3300XL 5/8mm proximitor probe?
Difference b/w SCADA & DCS
What should be the stanchan Height for installation of Smoke detector & toxic gas detector in field,according to qatar standard
A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)