Level in tank under vacuum (Ex: Condensate Tank of Power
Plant)is measured using D. P. type level transmitter. Tank
is subjected to vacuum of 755mmHg. Is it possible to fill
wet leg ( i.e. leg connected to top of vessel with low
point of D. P. xmtr) with water?. Are there chances of
water getting sucked under vacuum? if yes, what is the
solution?
Answers were Sorted based on User's Feedback
Answer / rajesh batham
we can make a loop system in wet leg so that pressure can be equal in both leg
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / varatha
no ..it won't suck. up to particular temp and pressure. we can fill by isolating the condensate pot
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / prashant mori
its only solution use remote diaphargm type transmitter.
or use displacer type transmitter.
| Is This Answer Correct ? | 0 Yes | 2 No |
pt range is -45 psi to 45 psi.friends can you give answer with calculation and with linerity scale like 0%,25%,50%,75%& 100%?
How to calibrate and check thermal mass flow meter of Make thermal instrument company inc model 60?
i am working in the automation company...i want to just know how actully pid control valves are tune????...
How does the "as-built" function benefit plant owner/operators?
how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).
Differentiate between ultrasonic flowmeter and radar type flow meter
Where can i take training in intools software for Instrumentation design??
how to convert % to ma
1 Answers Flour Tech Engineers (P) Ltd, Techint,
how to calibrate load cell
why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.
Draw a group of instruments interlocked to a Pump & Motor?
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)