Answer / nitish katoch
no we can we can only calibrate measuring devices..its
calibration is only depend upon its design
| Is This Answer Correct ? | 7 Yes | 3 No |
Answer / velu
Actuator can be calibrated. for example Pneumatic Actuators
are used in control valves. we have to calibrate the
Actuator as per name plate depend on the actuator size and capacity(call us bench set) for proper opening
and closure of the valve.
| Is This Answer Correct ? | 4 Yes | 0 No |
Actuator can be calibrated. for example Pneumatic Actuators
are used in control valves. we have to calibrate the
Actuator between 3-15psi pressure range, for proper opening
and closure of the valve.
there is nothing saying whether field
devices alone can be calibrated. All process control as well
as sensing devices should be calibrated periodically.
| Is This Answer Correct ? | 4 Yes | 3 No |
You cant calibrate an actuator, you can just do setting.(
setting means better performance and more accurate ).
But calibration is the process of measuring the actual
performance of an instrument-under-test using lab
instruments ( or we can do this in the field ) that in
turn have significantly better performance than the
instrument-under-test. The measured performance is then
compared to published data sheet specifications. If observe
the instrument to be out-of-specification, instrument must
adjust and re-test .( for example we can do calibration for
a thermocouple or pressure transmitter )
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rcsp2689
Inprocess loop measuring Ends can be calibrated . ie., Sensors.. Where else Actuators are Final contol element / Output devices.
| Is This Answer Correct ? | 1 Yes | 1 No |
What is the meaning of Dry contact and Wet Contact related to to sensors?
types of cable..? Use of every types of cable..?
Any Transmitter Range (Span value) start from 2?
Working principle of vibration sensor?, Type of vibration sensor? , Can we use vertical instead of horizental or vice versa?, if not Reasons?
how to draw a flowchart for swapping two numbers using bit wise operators?
WHAT IS MEANT BY SUPERVISORY CONTROL?
why do we use 4-20 ma current why cant o-20ma
what is Micro-switch and where it is used......?
what is shutoff dp? why is it important for selection of a control valve?
What is 1:1 redundancy ?
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
What pressure transmitter.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)