1.what is the role of proportional comtroller in pid
controller?2.How do u calibrate the control valve?
Answers were Sorted based on User's Feedback
Answer / krishna
proportion control function is to maintain constant offset
between set point and process variable .but it cannot remove
the offset. it makes the p.v to oscillate between high and
low limits.
There are two things required for calibrating control valve
1)pneumatic tester ( signal :0.2 to 1kg /cm2
)
2) air supply source according to design of valve.
initial for 0.2 kg.cm2 valve should be (open or close )
according to ATO ATC) )
THEN CHECK POSITION AT 25 50 75 100 % OF VALVE ACCORKING TO
SIGNAL TUNE WITH POSITIONER
| Is This Answer Correct ? | 20 Yes | 1 No |
Answer / www.islamqa.com
Actually we can make it simple:
# P:
it's a controller gain which modify the controller o/p
proportional to the error.
# I:
it's a controller gain which modify the controller o/p
proportional to the integral of the error.
# D:
it's a controller gain which modify the controller o/p
proportional to error rate of change.
We have 4 parameters in our control loop to focus on:
1 - the rise time: the period of time during which the pv
get 90% of the desired sp value
2 - max overshoot
3 - settling time: the period of time during which the pv
get the desired sp value and saturate.
4 - error/offset
we can get it clear from this pic:
http://controls.ame.nd.edu/ame437/S2003/hw1/specifications.j
pg
Now we will take a look about the effect of each controller
gain on these parameters:
# P gain:
decrease rise time
increase max.overshoot
increase settling time
decrease error (but not eliminate)
# I gain:
decrease rise time
increase max.overshoot
increase settling time
eliminate error.
# D gain:
no effect on rise time
decrease max.overshoot
decrease settling time
decrease error.
the previous is guidelines to be in background while
dealing with PID,but they are not sharp limits.
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / prashant
proportional function is take place an action to maintain
the pv proportionaly to error in p.v . but an offset error
is sustained , that will be reduced by integral funtional.
calbration of control valve :::
1. check the pneumatic pressure of regulator
2. give the 4-20 ma to check the strock of c/v
3. if storck is not achieving then adjusted by zero
& span adjustement
| Is This Answer Correct ? | 9 Yes | 4 No |
what is ABB DCS SYSTEM?
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
How to convert ma to mv? Resistance 250 ohm is connected in series or Parallel?
what is the input of ph sensor and meter during the calibration time and what is the output?
what is linerity and non-linearity?
what is difference between 3 wire and 4 wire RTD sensor?
12 Answers HTA Instrumentation,
What is DCS and PLC scanning time?
can any one tell me when ongc placement test and its forms is available????/ pls tell me if u know
what is field bus system. need defination
Wht should be the ratio of natural frequency (Fn) to wake frequency (Fw) and wht if goes above the rato limit?
How to calibrate electronic type level switch low?
i am working in the automation company...i want to just know how actully pid control valves are tune????...
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)