What are the problems faced while testing HART instruments?
Answer / carl_ellis
Failure to connect with HART can be a laundry list of
issues, the most common of which is the
lack of minimum 230 ohm resistance in the loop.
Other reasons can be
- HART probes connected across the DC power supply, not in
the loop
- failed DC power supply
- electrically noisy DC power supply
- HART modem lacks installed PC driver or internal setup
(serial modems were touchy)
- HART device not at expected HART address (address zero for
point-to-point comm)
- device does not have HART option or HART option has been
disabled.
- HART option replaced by different fieldbus comm card (it's
happened! !)
- Connecting across the test terminals on a pressure
transmitter where there's no HART signal
- HART communicator is dysfunctional or its batteries are
discharged
- lack of DD in communicator/program limits access to the
common commands
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the difference between 2 wire and 3 wire RTD- application wise,cost effectivity?
what is the standard controll pressure
what is modbus & what signals are taken through it
Any can guide for QA/QC Inspector in oil & gas region, the procedures, formats standards, design criteria, i search in all enginees but i can't found wat i need?????????
4 Answers Aramco, Asian Paints,
What is the use of temprature compensation?
What is the relationship between GAIN and PROPORTIONAL BAND.
1 Answers Kharafi National, Sabic,
how do i tune dearator pr control valve using PID. we set the set point is 0.6kg/cm2 now i want 0.5 to 0.7kg/cm2 limits so what should i give p,i,d values. then pls explain how do set pid values for control valve tuning?
0 Answers SEWA, Sharjah Electricity and Water Authority SEWA,
Differentiate between ultrasonic flowmeter and radar type flow meter
what is mean by hot loop and cold loop testing, whts different between both
Explain why plc require in analog input 4-20amp & 0-10 volt?
Dear Friends, we are planning to design Power distribution and Fiber optic in the same cabinet.Like Front side Fiber optic and Rear side Power distribution.Is it any possibility of problem occurs like interference etc? Your answer is highly appreciate.
Why some transmitter shows flow in MMWC and some in TPH?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)