Answer / carl_ellis
Failure to connect with HART can be a laundry list of
issues, the most common of which is the
lack of minimum 230 ohm resistance in the loop.
Other reasons can be
- HART probes connected across the DC power supply, not in
the loop
- failed DC power supply
- electrically noisy DC power supply
- HART modem lacks installed PC driver or internal setup
(serial modems were touchy)
- HART device not at expected HART address (address zero for
point-to-point comm)
- device does not have HART option or HART option has been
disabled.
- HART option replaced by different fieldbus comm card (it's
happened! !)
- Connecting across the test terminals on a pressure
transmitter where there's no HART signal
- HART communicator is dysfunctional or its batteries are
discharged
- lack of DD in communicator/program limits access to the
common commands
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
In bimetallic temp. Gauges why does metal strip bend? Why do we use low expansion factor metal and high expansion factor metal in bimetaliv strip?
1 Answers Process Control Technologies,
give some question relative instrument fitter?
what is the difference in Kg/cm2 and mmwc?
yogokowa field bus system transmitter all's we are geting IOP fault in Contiunes please help me fine how we can normal the broblems?
Good evening all I need a small favour regarding reliance paper i wanna probable sample papers(e&i) of reliance. if any of u have any idea about dis then plz mail me back.i belongs to electronics and instrumentation engg.so i need e&i papers. thanking u....
Square root calculation for dp flow transmitter?
what is the use of shield cable?
What is the procedure of mounting new positioner on pneumatic control valve?
The wire is disconnected from the temperature sending unit (magnetic gauge). A voltmeter connected to the wire reads 0v. What does this indicate?
how to define range of dp level xmeter in open tank
Dead weight tester & comparator for calibration , which is more accurate , what is the application.
1 Answers Bapco Bahrain Petroleum Company,
What is instrumentation measurement?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)